Why Harmonics in a three phase motor ?
recently I measured the electrical parameters of a 50 HP motor that has a wye delta starter , no electronic at all and my Fluke power meter registered 60% THD-R, Why ?
Thanks in advance for any tip you can tell me on the subject
RE: Why Harmonics in a three phase motor ?
I can only think of a few possibilities
- thd-r is some weird parameter that I don't understand.
- your meter is screwed up.
- your motor is at no-load and you have an extremely high or unbalanced voltage applied, pushing the core very very far into saturation
Then again I may just be totally missing something.
again what could be the reason ? harmonics created by capacitors ¿? I doubt it
I think most utility service standards do not include "quality" of power delivered unless there a special service contract provisions for such -- but if there are quality problems generated by a customer, they can and will impose corrective measures at a cost to the one creating the problems...
As far as power quality and harmonics, I believe IEEE519 addresses this from the users end.
Also, the capacitors may be creating a resonant condition which will act as a sink for any other harmonic currents in the system.
If it is voltage, you have a real problem and nothing much would be working right at your facility.
Assuming its the current, measuring harmoincs at no load of a motor is meaningless. You are analyzing magnetizing current which has very low (0.2 or less) power factor. 60% THD on no load means nothing. Please measure THD at full load, 75% and 50% loads which is a more meaningful analysis.
I do not know what THD the magnetizing current should read, But whatever it may be, I would not attach any singnificance to it,unless I see high THD in loaded condtion.
You may also wish to measure Voltage THD on the supply bus when the motor is off.
Note this assumes that you are measuring upstream of the power factor correction.
Best regards,
Mark Empson
http://www.lmphotonics.com
It's about the same as asking why the efficiency of your unloaded motor is 0%. It doesn't (necessarily) mean that your motor sucks -- it's just a meaningless number.
Let
FLA = Full load amps
INL = no-load current as fraction of FLA.
(assume INL = 25%)
Harmonics = rms of harmonic content as fraction of FLA.
THD_NL = no-load THD (given as 60%)
THD_FL = full-load THD
THD_NL = 0.6 (given)
Harmonics = THD_FL*INL = 0.6*0.25 = 0.15
THD_FL ~ sqrt(1^2 + 0.15^2)-1 = 1.011 - 1 = 0.011 ~ 1%
Also as I remember there are two definitions of THD. One divides by the fundamental and one divides by the total. Doesn't normally make a big difference but it does when dealing with THD=60%.
I haven't got time right now to figure out a better answer. I'm pretty sure you will be surprised at how low the full-load THD will be. Anyone else want to try?
Harmonics are always present whenever an AC current is flowing, even without the help of electronics.Your measured THD of 60% seems extreme under any conditions.
Some motors with Low loads or no loads can have asyncronous magnectic fields causing fairly high umbalances at no load.
I don't know if the THD could get as high as 60% under those conditions.
GusD
A few more facts may help: what type of motor is it, what is the rated speed, what type of load is it driving, what is the actual speed of the shaft, how balanced are the phase voltages and currents, what about the readings on other similar motors and other circuits in the plant? All of these affect the voltage and current waveforms.
If your capacitor is connected at the motor terminals, could you disconnect it and then check your current again ?
The only influence of the capacitors that I know can be to increase the (fundamental) voltage. Higher voltage pushes further into saturation and causes more current harmonics.
that was exactly I was thinking.