Rewelding of pipe joint to boiler

Rewelding of pipe joint to boiler

Rewelding of pipe joint to boiler

(OP)
would it create any problem if we reweld the same joint (of one pipe 2" to the shell of boiler) which has already been welded (repaired by welding)four time with the gap of one year , steam is leaking at the moment , i need very urgebt response  

RE: Rewelding of pipe joint to boiler

I have been out of the power industry for some time but I do recall some of the do's and dont's. Typically, if it is not fixed after three attempts it is replaced. I am not sure if you are talking about a butt joint from a pipe to a nipple or a saddle weld from the boiler to the nipple. If you are not stress relieving the joint after you attempt to repair it the material is still prone to cracking. You will need to be a little more specific with the question to get a more informed response.

RE: Rewelding of pipe joint to boiler

Contact a Qualified Repair Firm. See current NBIC. You could have a design issue of merely workmanship.

RE: Rewelding of pipe joint to boiler

If you are in the U.S. and insured there is person called the "Authorized Inspector" that works for the insurance company that can offer assistance with your problem. They are well versed in the ASME Codes along with the NBIC. Both of these codes address your issue in great detail.

I think you will need assistance.

RE: Rewelding of pipe joint to boiler

Your job appears to be to get the boiler back in service as soon as possible.  The repair may be made under NBIC rules.  The real problem is to determine cause of repeated failures. Is is welding related; e.g., lack of preheat - noting that the drum is very thick compared to the 2" pipe and poses an immense heat sink.  Or is it design related; e.g., water hammer.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources