Connecting house to 3ph generator

Connecting house to 3ph generator

Connecting house to 3ph generator

(OP)
Hello list,
  Can an engine driven 3ph generator be hooked up to a house and keep the phases balanced?  I can see that two phases are used in the normal connection, but how is the third phase utilized?  I have searched FAQs and the archives, but may have missed a previous discussion.  I apologize if this is a repetitive question and if so, could someone recommend a thread to search out?

Thanks,
Phil

RE: Connecting house to 3ph generator

While you will not be able to balance the phases, as long as you do not exceed the rating of each phase, and run a full size neutral, this should not be a problem.

Specially if this for a residential application and will only be used in emergency.

Question should be  'is it necesarry to balance this generator? ' and I am sure you will get a barrage of answers telling you what you 'can' do convert a 3 phase to single phase, but won't be practical and you dont have to do it.

May be your neighbour can use the unused phase and have a win win situation:))

RE: Connecting house to 3ph generator

There’s no way I have found to get full generator capacity {kW-kVA} on a 12-lead 3ø generator with an “Edison” 120/240V 1ø 3-wire load.  

Best that can be expected is about 2/3 capacity, and  a corresponding unbalanced load.  For a plain-vanilla 12-lead stator..

“L1” — T1 & T7
 “N” — T4, T10, T5 & T11
Bolt and Tape — T2, T8, T6 & T12
“L2” — T3 & T9

That’s from memory, so may not be accurate.  Some have referred to this as a LeBlanc connection.  {Some consider the LeBlanc connection a way to get 1ø power to present a balanced load to a 3ø source through a transformer set, but that is not correct.}  

Adjust the voltage regulator for 120V/coil.
    

RE: Connecting house to 3ph generator

(OP)
Thank you both for the feedback.

Phil

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources