Above ceiling as return plenum

Above ceiling as return plenum

Above ceiling as return plenum

(OP)
Is it normal to use the area above a suspended ceiling as a return plenum? We have a large building with several rooms and zones with no return ducting at all. It seems to me we are picking up a lot of heat in the summer (losing heat in winter). Just curious.

RE: Above ceiling as return plenum

It's quite normal to use the ceiling void as a return air plenum.  It saves on return air ducting as well as the thickness of insulation required for the supply air ducting.  If it's ducted return, then the ceiling void  can get quite warm/hot and if the insulation is not done properly, (more so, if there is exposed roof above) can cause condensation problems.

RE: Above ceiling as return plenum

It also reduces the supply air requirement because the plenum heat gain goes to the return airstream, not to the conditioned space. However note the following:
-Wiring in the plenum must be plenum rated (Teflon insulated)
-Partition must not go all the way to the slab above unless transfer air openings are provided
-Transfer air openings must be sized for minimal pressure drop, about maximum 300 FPM velocity to minimize pressurization to effect transfer air flows. Sometimes a transfer fan may be required.
- Maintain fire/smoke rating of rated walls by providing fire or combination fire & smoke dampers where required
- Avoid sound transmission. May have to use transfer air silencers or ducts with elbows & acoustic lining.

RE: Above ceiling as return plenum

I agree with both above. It's very normal. At the same time partitions and above-ceiling wall separations and requirements for fire rating systems become more important.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources