Induced Voltages by Power Lines
I'm looking for a formula that would calculate the induced voltage on a pipeline trace wire that is running parallel to a high voltage power line.
RE: Induced Voltages by Power Lines
Or where I could find it would be great also.
Terence483:
You can use the method of IEEE 575, to calculate the required induced voltage as following.
Ep=jw(Ib)*2*(10 power (-7))*{0.5*ln(Sap*Scp/Sbp)+jSQRT(3)/2*ln(Scp/Sap)}
Where:
Ib:Current in conductor b
w:angular frequency = 2pf
Sap:axial spacing of the parallel conductor and phase (a) conductor
Sbp:axial spacing of the parallel conductor and phase (b) conductor
Scp:axial spacing of the parallel conductor and phase (c) conductor
Its assumed that the phase rotation is such that:
Ia = a Ib
Ic = a2 Ib
Where
Ib = Io (1+j0)
Where
Io=magnitude of the load current.
If it is useful for you, pls. mark it by * as helpful.
Bye
Tawakol