Use of a Control Valve as a flow meter??

Use of a Control Valve as a flow meter??

Use of a Control Valve as a flow meter??

(OP)
We are having problems with some ultrasonic flow meters installed recently on the oil outlet of a first stage seperator.

It would appear that we are getting sufficient water or gas in the oil to prevent the meters from working.

As a quick fix for this we are looking to use a control valve mounted downstream of the meter to approximate the flow vs %open.

Has anyone used this before ?  What sort of accuracy was achieved?

We are looking to calculate the flow based on the Cv of the valve.

Any helpful tips??

We can program the DCS to calculate the flow.

Leggy

RE: Use of a Control Valve as a flow meter??

Hi,

Do an internet search on "NELFLOW".  Such a product is commercially available.  Their literature should help in identifying the accuracy.

BCD

RE: Use of a Control Valve as a flow meter??

(OP)
Thanks, I have looked at this and it could be useful.

What we are trying to do is use an existing 12" Globe Valve from Fisher rather than shut in to change out.

RE: Use of a Control Valve as a flow meter??

accurracy is +/- 20% unless you have a valve that has calibrated in a flow lab.

just put a valve down stream of your current meter. this can create back pressure that will help prevent gas from coming out of solution and allow for proper dis-engagement in the separator. It does not have to be calibrated, the meter should work fine.

The caveat is that your piping system has been appropriately sized and in such a way as to keep the pipe liquid full..

good luck

RE: Use of a Control Valve as a flow meter??

Even calibrated in a lab, a proportional valve is never more accurate than around 15%.  You could probably get the backpressure benefits with an inexpensive orifice plate between two flanges downstream of the ultrasonic meter.

David

RE: Use of a Control Valve as a flow meter??

leggy,

You can use control valve to measure flow if you have critical flow condition and there is no phase change which I think is not possible since you have saturated condition.

An alternative is to relocate your US flow meter way below your vessel to prevent gas breakout. Three to four meters below normal liquid level and preferably flow direction of ultrasonic meter is downwards.  

Also opt changing your ultrasonic meter to coriolis meter.  There is no minimum straight length requirement for coriolis meter and can accept gas breakout.  Water cut, volumetric and mass flowrate, totals can be displayed and accessed in some coriolis meters.

Regards,

209larry

RE: Use of a Control Valve as a flow meter??

I know Valtek (now FlowServe) make a control valve with pressure and temperature sensors in it for measuring flow, except I do not know how good it is.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources