Need vibration limits on large AC vertical motors

Need vibration limits on large AC vertical motors

Need vibration limits on large AC vertical motors

(OP)
I have a large AC motor (1750HP, 1800 rpm) installed vertically. every time it trips the vibs goes up by 0.1ips
Started with 0.3ips after two trips 0.5ips. how long can I continue before s/d the motor and get it balanced.

RE: Need vibration limits on large AC vertical motors

bopsyseng, How or why is this motor tripping out? If motor 1x goes up every time this motor trips, then there must be an electical problem in the motor. Something must be moving or loose to allow an increase in vibration. Is the phase on the vibration stable or is it shifting with each trip?

Tophat

RE: Need vibration limits on large AC vertical motors

(OP)
Motor was balanced before installation. One time motor tripped due to ground fault, second time it tripped due to blackout (08/14/2003). Motor also has a Mechanical Seal.

RE: Need vibration limits on large AC vertical motors

Tripping out should not cause an imbalance problem. If no phase history then try to start one. If level increases to .7 ips then I would recommend inspecting motor, coupling, and driven unit. What is unit driving and what are levels on the driven unit. Had a call out on a vertical motor one time due to high vibrations. It was driving a pump they had not taken readings on. The bearings in the pump were trashed. Problem solved with repairs.

RE: Need vibration limits on large AC vertical motors

(OP)
The vibration analysis shows only one variable sine curve. We assume it may be due to imbalance. The bearings appear to be in good shape (based on sine curve). We did recommend 0.7ips as cut off vibs to remove pump from service. The vibs at present are stable at 0.5ips. We will try to balance in a week or so.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources