Explanation of NEC article 680.26 section 3

Explanation of NEC article 680.26 section 3

Explanation of NEC article 680.26 section 3

(OP)
What is the significance of the 4" measurement with regards to isolated parts?

RE: Explanation of NEC article 680.26 section 3

If you are refering to 680.26.B.3, 4 inches is the largest dimension permitted for an isolated metal part within the swimming pool that is not required to be bonded. It is not a clearance requirement. For swimming pool installations, I strongly recommend consulting with a licensed electrical engineer experienced with swimming pools.

RE: Explanation of NEC article 680.26 section 3

(OP)
But why 4"?  Why not 5" or 6"?

RE: Explanation of NEC article 680.26 section 3

I assume it's because they feel like it is unlikely for something that small to accidentally become energized or that someone may be in contact with it.

RE: Explanation of NEC article 680.26 section 3

(OP)
The whole article reads:

"All metal fittings within or attached to the pool structure shall be bonded.  Isolated parts that are not over 100 mm ( 4in.) in any dimension and do not penetrate into the poll structure more than 25 mm (1 in.) hall not require bonding."

Does that mean that if an isolated part is over 4", but does not penetrate the pool structure by more than 1", it also does not require bonding?

RE: Explanation of NEC article 680.26 section 3

Read it again, it's pretty clear:  If it pentrates by more than 1" then it does require bonding.

RE: Explanation of NEC article 680.26 section 3

(OP)
But what if it is larger than 4" and does not penetrate by 1"?  Does it still require bonding?

RE: Explanation of NEC article 680.26 section 3

The rule has 3 conditions for not requiring bonding, all must be met:

1.  The part must be isolated.
2.  The part must not be larger than 4 in.
3.  The part must not penetrate into the pool structure more than 1 in.

If any of these conditions are not true, bonding is required.

RE: Explanation of NEC article 680.26 section 3

Oops, sorry, I was typing too fast, my intended post was:


If it pentrates by more than 1" OR if it's bigger than 4" then it does require bonding.

If you violate EITHER condition, then you need to bond it.

RE: Explanation of NEC article 680.26 section 3

rjohnston
I read your other post in the corrosion forum.
What are the large structures for, or can't you say?
The corrosion guys seemed to have got a handle on the corrosion potential.
Is it a swimming pool or do we evacuate the fish because of zinc poisoning?

RE: Explanation of NEC article 680.26 section 3

(OP)
rnd2

It is a pool (ie. chlorinated water).  People will be swimming in it.  There will be no fish.

As far as what the structures are lets just called it a large mechanical device with a lot of moving parts.

The SST pins are at the pivots.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources