Augered Piles
Augered Piles
Please advise where can I find information on the characteristics, performance, and design of augered cast-in-place concrete piles for elevating a residence type building
RE: Augered Piles
RE: Augered Piles
RE: Augered Piles
The other type of augered pile I'm familiar with are straight shafted piles and they can be 40 or 50 feet long. They can be 12" to 36" diameter and are usually designed for skin friction but sometimes for end bearing if good material and not too deep. Due to differences in soil shear stiffness compared to compression stiffness, shear and compression are not generally used in tandem.
A geotekkie should be able to provide you with bearing values or skin friction values. Skin friction I've encountered has varied from 250psf to 450psf and bearing pressure from about 4000psf to 15,000psf. For end bearing caissons (big belled piles) bearing on glacial till has been as high as 40Ksf (founding surface inspected by geotekkie) and have used 20Ksf on the same soil (non-inspected for smaller shafts)
Larger shafts that are inspected require sleeving with a steel pipe and a minimum sized sleeve (Ministry of Labour Requirement and possibly OSHA or some other authority has a similar requirement) The sleeve is withdrawn as the concrete is placed.
If the soil is competent, it can provide the lateral support. Concrete strength is often 20 MPa and 4" or 5" slump. Some clays have high sulphate and require Type 5 cement. If subject to freeze and thaw, then 5% to 7% air. I've used caisson caps of higher strength air entrained concrete over caissons using a lower strength, non-air entrained concrete.
Reinforcing steel is nominal (I usually use 1/2%) with sufficient ties to keep the bars in place and additional bars at top
Reinforcing steel may not be full length.
I usually vibrate the top 10' to consolidate the concrete against the soil as well as improving bond to reinforcing steel (former is main reason).
RE: Augered Piles
KAM is describing an augercast pile, constructed with a medium diameter hollow stem auger. The auger is placed to the required depth and grout is pumped into the hollow annulus, uner pressure, while the aguer is slowly/carefully withdrawn. I have also had experience with the contractors listed. They are very helpful.
dik is describing (and giving good recommendations) for a augered pile (known in some areas as drilled pier, caisson, cast in place pile) which he describes.
The Deep Foundations Institue will also have good information for this type.
RE: Augered Piles
I've not encountered this type of pile. Looks like it could be easier to use with granular materials that would otherwise slough into the hole. Any idea of what load capacity or the manner of calculating the load capacity. I'll check with a couple of local foundation contractors to see what info they have.
RE: Augered Piles