Hi there
We are using an drive on a hoist for a depalletiser. When 'down' is selected the drive trips on over voltage. Probably due to the weight causing this. Can one set something on the drive to prevent this from tripping out? Or any other suggestions please?
We are using the Allen Bradley Powerflex4   3.7KW
Thanks

RE: Over voltage fault on drive.

Sounds like you need a break chopper. The back EMF from the suddenly unloaded motor ("down") is causing your capacitor voltage to increase. The chopper will momentarily short the plus and minus of the caps through a resistor to bring the voltage down. Also, check your parameter for the over voltage setting and make sure it is correct. If it's set too low, you'll get nuisance trips.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources