Double Angle bending

Double Angle bending

Double Angle bending

(OP)
I am trying to calculate the allowable stress for double angle beams used to support utility piping.  The "stem" of the double angle is turned up, i.e. the stem is in flexural compression.  I have some literature on wt shapes in this configuration, seems like a lot of derivations just to arrive at 0.6Fy for the allowable stress.  Just wanted to know if anyone had come across this and how to arrive at the allowable stress relating to lateral torsional buckling.

RE: Double Angle bending

let me know you are finding allowable stress as per which country code. Please specify. and also let me know how double angle is connected ( eg. back to back )

RE: Double Angle bending

(OP)
The double angles are suspended from each end with 3/4" diam threaded rod (angles are approx 4'-6" lg.  The angles are connected with 7/8" plates at the ends and at midpoint.  The design will be based on AISC ASD.

RE: Double Angle bending

Why do you need a double angle section for pipe support?
I can't visualise any specific advantages.
Why don't you go for a channel or I- beam section? Ligher
and easier to connect, and you don't have analysis and
design problems!

Hariharan

RE: Double Angle bending

Under the British code, BS5950 there is a fair bit of work to do to get the allowable bending stress for a double angle member because it is not often used in bending. So I wouldn't be surprised if there are a few derivations to go through to get to this figure. However I wouldn't make any assumptions about the result as it could vary a great deal depending on span and angle size.

Carl Bauer

RE: Double Angle bending

I agree with Hariharan...why not consider another section.  At the least, turn the angles over such that the leg-down is in bending, not leg-up.  This makes it easier to attach the pipe, gives a larger bearing area for the pipe and negates the "stem" compressionissue.

Ron

RE: Double Angle bending

I agree with Hariharan....change the section if you can.

Otherwise, turn the angles over such that the legs are turned down.  This will make allow more bearing area for the pipe, make it easier to use "U"-bolts to secure the pipe, and negate the "stem" compression issue.

Ron

RE: Double Angle bending

(OP)
Thanks for the input, I have found the section in AISC ASD ninth edition.  Starting on pg 5-309, this section covers angles in flexure.

RE: Double Angle bending

If you can do what Ron boss and  Hariharan suggested, you will have a safer system, easier connections and lesser calculations to make, and guys who galvanize or paint will thank you,as agreed by friends above.

However while at the subject you might also want to take a look at this article:

         Design of single and multiple Angle columns and beams, by Cedric Marsh, Journal of Structural Engineering, July 1997 page 847-856

That is for reference. But we frequently design pipe racks and we use channels or I-beams. I assume your utility is real small.

Good luck.

RE: Double Angle bending

(OP)
This installation is for very small (< 2") pipe and conduit.  It is for a mechanical contractor doing construction in and existing building.  I believe they have a surplus of angle they purchased for their piping/conduit runs.  I, too, typically use wide flange or channels in piperacks.  I wouldn't even consider this a piperack.

Thanks for all the input.

Ag89

RE: Double Angle bending

ag89...one more comment, now that I think I understand a bit more about your application.

You might consider a pre-fabricated product that is both structurally viable and contains a spun aluminum flashing flange to allow better roof penetration connection.  These are known as Thaler supports (Thaler is one brand, but I believer there are others).  Check their website at:

http://www.partsdome.com/thalermetal/default.asp?ShopperCurrency=USD

I have used these before and they are high quality.

Ron

RE: Double Angle bending

Good grief, guys!
Just use "unistrut" like everybody else does.
Besides , it's cheap, and comes in a variety of sizes and strengths.

Rod

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources