WYE source to a DELTA transformer primary?
2

WYE source to a DELTA transformer primary?

WYE source to a DELTA transformer primary?

(OP)
A quick question on power transforming:
  It appears that our building is supplied with 480 3-phase power in WYE form.  That is, a four-wire system.  We just moved into this building and are in the process of hooking up our power transformers to step down the power for 220 3-phase.  But on close inspection we discovered that our transformer is a DELTA-WYE tranformer (DELTA Primary).  If our power source is WYE, will there be a problem connecting to the DELTA primary of the transformer?  What is done with the WYE-neutral?  Is it a normal practice to leave this neutral unconnected?  

RE: WYE source to a DELTA transformer primary?

If your transformer is 480V Delta primary, and 220V Wye secondary, yes it is common practice to not use the neutral provided at the 480V Wye service. Simply bring the three phase conductors (and ground), and follow the code requirements for your location.

RE: WYE source to a DELTA transformer primary?

Suggestion: A chain connections of transformers from upstream to downstream:
1. primary delta, secondary wye (grounded) - upstream transformer, e.g. 4.16kV-D/480V-Y
2. primary delta, secondary wye (grounded) - the first downstream transformer, e.g. 480V-D/220V-Y
3. primary delta, secondary wye (grounded) - the second downstream transformer, e.g.  220V-D/110V-Y
4. etc.
is considered the industry standard since it:
1. Breaks the zero sequence path
2. Solidly grounded wye establishes good system grounding
3. It is good for the secondary multivoltage system, e.g. 380Vphase-to-phase/220Vphase-to-neutral
4. Etc.

RE: WYE source to a DELTA transformer primary?

(OP)
Thanks for the help, DanDel and jbartos!

RE: WYE source to a DELTA transformer primary?

This is very normal configuration. No neutral is connected to the primary side of a delta-wye transformer. But a equipment ground condcutor is required.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources