what is the minimum size for a bonding jumper from the secondary side of a Y transformer to 4-wire 480V switchgear - conductors are rated for 2500A?  The loads are all three phase balanced.  Also, should the size of the jumper from the transformer secondard neutral to ground be the same size as the jumper to the switchgear?

RE: neutral bonding jumper

Where is your location? The NEC 250.28(D) specifies this jumper(if I read your post correctly), but I believe it only applies to the USA.

RE: neutral bonding jumper

Suggestion: If conductors are rated and protected by 2500A overcurrent protective device, then the minimum size of equipment grounding conductors for grounding raceways and equipment would be 350kcmil copper; see NFPA 70-1996 Table 250-95, or visit
http://www.nfpa.org
for NFPA 70 National Electrical Code.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources