Finding Power Factor of a 3 phase motor
Hello everyone!
I am having a difficult time determining the Power Factor of some older 3 phase motors. The pf is not listed on the data plate. I have looked up formulas about arriving at power factor with KW's and KVA known. I can't figure my KW's correctly because I don't know my power factor, and I can't find the power factor without the KW's. Is there a way I can find all of this out by finding the inductive reactance to actual (measured) resistance ratio of the motor windings? Can the power factor be found by HP or some other listing on the data plate?
I'm really having a tough time of this. It's starting to give me a headache. I would be happy if someone could even direct me to a website that would step me through a formula.
Any help will be greatly appreciated.
Now ya know why I picked 3phasedaze as my user name! HA HA.
RE: Finding Power Factor of a 3 phase motor
power factor = HP*0.7457/(sqrt(3)*If*V)
The above will give you the power factor at full load. Motor power factor varies with load, power factor tends to get lower with reducing load. If you do not have motor data, you can only determine power factor by measurement.
the motor efficiency is missing from your calculation.
pf = kw /[sqrt3*V*I*efficieny]
That makes it seem so simple. I like simple.
Thanks for the help.
If all you need is to know what power factor correction capacitor should be connected to your motors, I suggest
capacitor (in KVAR) = 1/3rd motor HP. For a 30 HP Motor - 10 KVAR, 10 HP motor - 3 KVAR and so on. In most cases, this simple thumb rule will suffice to bring overall pf to near about 0.9.
By the way, does it take 3 capacitors for each 3 phase motor, or are there '3 phase' capacitors for one motor?
You use 3-phase capacitors (having three terminals)which are standard products.
Great! That makes my task a lot easier, and less time consuming. You've been more than helpful, and very patient.
3pd
Allow me to make a couple clarifications to your Aug 18, 2003 post .....
"kW = HP * .7475 / efficiency"
1) The constant is .745699 which is normally rounded up to .746
2) When converting kW (a unit of power) to HP (a unit of power) .... efficiency is not a factor.
Where it sometimes gets muddy in these discussions is the failure to differentiate between input and output terms.
The unit of power on a motor nameplate is that of the motor mechanical shaft power.
Motor electrical input power in kW ÷ 0.745699 = electrical input power in HP units.
Likewise.....motor shaft mechanical power in kW ÷ 0.745699 = motor shaft mechanical power in HP.
Now then....to the issue of efficiency...
When determining the Output Shaft mechanical power from the input elect power, you need to use efficiency in the calculation as you correctly stated.
I raise this distinction because the original question was that of determining Power Factor which is a factor used in determining the input electrical power.
As you correctly stated, the INPUT electrical kW is determined by multiplying the OUTPUT shaft mechanical HP by the conversion constant (0.746) and dividing by motor efficiency.
http://www.designnotes.com/CIRCUITS/pwrfact.htm
http://www.rudrashakti.com/products.htm
http://www.tpub.com/doeelecscience/electricalscience2169.htm
etc. for more info
Thank you for the clarification on this confusing point. You are absolutely correct.
1. My apologies for the dyslexia. '.7475' should have read '.7457'
2. The preceeding discussion was regarding the relationship between nameplate (shaft output) horsepower and input kW which must include the efficiency.