Hi!

Interested to hear of anybody’s experience with silicone insulators. Traditionally our substations have used porcelain insulators (for historic reasons). Recent breakage’s of porcelain has highlighted the fragile nature of the material and the possibility of a serious failure occurring is frightening. Silicone would not be prone to breaking or fracture during transport and installation.
What is anybody’s experience with silicone? Pollution is not a problem, although I would prefer to stay away from silicone insulators with GRP cores.

Thanks

Regards

RE: Silicone v Porcelain Insulators

MY only experience is from using polymer insulators on some units that we manufacture, based on customer specifications. We have not had any reported problems with them in the field. In the US, we have seen the number of utilities specifying/accepting polymer insulators on the rise. They are used a lot in California, due to pollution, the reduction in need to live-line wash, and seismic concerns.

RE: Silicone v Porcelain Insulators

Silicon insulators are extremely lightweight (approximately one-third porcelain weight) and easy to handle. Silicon insulators are self-cleaning, fire and UV resistant and will not fracture or break if dropped.

RE: Silicone v Porcelain Insulators

(OP)
Thanks for the info!, but as the rubber is flexible (manufacturer quotes full recovery after 90 deg. bend) is there a danger under short circuit conditions of the conductors pulling apart and causing havoc? has this occured anywhere and prompted a rethink on the use of polymer insulators ?

RE: Silicone v Porcelain Insulators

In the early 80's we began using polymer insulators on 69kv transmission due to breakage of porcelain post insulators occuring during seasonal temperature changes. Today we use polymer insulators for most applications relating to transmission and distribution lines. Additionaly we use polymer as bus supports in substations and for line take offs. We have had very good experience with the Ohio Brass polymer insulators. We also use their polymer MOV arrestors.

RE: Silicone v Porcelain Insulators

In the mist belt of the west African Coast we have changed to "Rodurflex" silicon rubber insulators on 33kV network and witnessed a remarkable improvement.  Heavy sand and dust storms followed by heavy sea mists and no more flashovers. They are well worth the money. Interesting find: one glass disc = $150, (min 3 in a string = $450), rubber strainer = $180.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources