4Pole Circuit Breakers in LV Substation

4Pole Circuit Breakers in LV Substation

4Pole Circuit Breakers in LV Substation

(OP)
Consider a packaged substation as follows:

Two 2.0MVA 10kV - 0.4kV Dyn11 vacuum cast resin transformers TA and TB (close bus coupled to the switchboard).
Two main incomer ACBs to off-load the transformers T9A and T9B
Low voltage switchgear section split into two buses Bus A (normally fed by TA) and Bus B (normally fed by Bus B)
Normally open Bus-tie ACB
400V bus is 4Wire (TN-CS system) with a solid busbar link between the nuetral bar and the earth bar



This is a pretty typical redundant unit substation. I have been asked for advantages in specifying the incomers and bus-tie as 4 pole circuit breakers.

Does anyone care to comment on the advantages/disadvantages of this?

RE: 4Pole Circuit Breakers in LV Substation

Somewhat difficult to comment without the sight of the SLD.

RE: 4Pole Circuit Breakers in LV Substation

if the distributed transformers are not operated  in parallel and connections between the substations are only used as transfer connections,  the connections may be configured as a five-phase TN-S  system  with  L1-L2-L3-N  and  PE.  Four phase switching devices (L1-L2-L3 and N) are ,however, required  in this case.  A Four phase  transfer  device is also required  if satellite  substations are supplied by  two  system  infeeds  in  a  TN-S  system.

Ref:Electrical Installations Handbook(Third Edition)  Wiley press(ISBN  3-89578-061-8)   or  Publicis press.  ISBN  0-471-49435-6  page:35  see  also  figure  there...

regards...

RE: 4Pole Circuit Breakers in LV Substation



1. There is absolutely no adavantage in using a 4-pole breaker in main CBs (between TX and switchboard). You always want your trasformer neutral and swithboard (system) neutral firmly connected and grounded at all times . It is Code in the USA.

2. While may be permissible is some cases, there is no good reason to use 4 pole tie circuit breaker. Even if you do so, the Neutral contact shall be over lapping type meaning while closing the 4p CB, the N closes before any phase contacts close and while opening the N opens after all phase contacts have opened.  This is again to maintain continuity of system grounding. Even momentary ungroudned system can cause funny behaviour in sensitive equipments.

3. Since the two neutrals are already interconnected thorugh the grounding connection, there is no point in trying not to solidy connect the neutral bus. A removalble link is sufficicent to isolate a transformer completely during a maintenance.

4. 4 pole breaker is an odd entity.

RE: 4Pole Circuit Breakers in LV Substation

It would simplify ground fault detection (if that's applicable to your situation). However the 3 pole tie breaker is a very common configuration and most manufacturers can handle it with some version of modified differential ground fault sensing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources