ACI 7.10.5.3 explanation needed

ACI 7.10.5.3 explanation needed

ACI 7.10.5.3 explanation needed

(OP)
I need some help fully understanding what this section is describing.  I understand that every corner and alternate bar should have support provided by the corner of a tie, but I'm unclear about the 6" or less.  Is 6" the max. spacing of bars when more than 4 are req'd by analysis?  What if I had a column similar to the one shown in the figure with 12 reinf. bars, except my bar spacing was 7 or 8 inches.  Would I need to add more steel to reduce the spacing?  

RE: ACI 7.10.5.3 explanation needed

You could either add column steel so that the spacing of adjacent bars is less than 6 inches or add ties so that each bar (with a spacing of more than 6 inches) is laterally supported.  Even if you add column bars every other bar needs to be supported so you're probably ahead if you add ties.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources