If exterior masonry wall is NOT being used as MWFRS,
should the wall be designed as cladding?
Thanks.
should the wall be designed as cladding?
Thanks.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Masonry as cladding
RE: Masonry as cladding
If the wall spans horizontally the contributory area be the length of the wall X the height of the wall.
RE: Masonry as cladding
1. When you design the CMU wall for wind load perpendicular to it (windward and leeward) design it as component and cladding. Also, make sure you design it to the end zone pressure (ASCE 7 zone 5) even if the wall is within zone 4.
2. Design CMU wall for uplift from the roof, which should be determined on the basis of MWFRS.
3. Design CMU shear walls for MWFRS pressures. Do not include the internal pressure because it acts in multi-direction and it cancels out.
I like to recommend that you get a copy of "Guide to the use of the Wind Load Provisions of ASCE 7-98 by Kishor Mehta and Dale C. Perry. It is available form www.asce.org
Good luck.