Impedance of power cable

Impedance of power cable

Impedance of power cable

(OP)
In the electrical specification of power cable, I found that the positive sequence impedance and zero impedance of 500 mm sq 132kV cable is lower than 500 mm sq 11kV cable. Is the impadance depends on conductor size or other parameters? Any expert can give me advise on this?

RE: Impedance of power cable

There can be small differences in resistance due to differences in the stranding of the conductors.  The differences should be pretty small.

You should also check to see what temperature is used as a reference point for both resistances given.  This can make a significant difference in resistance.   

RE: Impedance of power cable

Impedance also depends on the cable spacing and shielding.  Larger spacing between phases increases the reactance.  Lower shield resistance increases the positive-sequence resistance because shield currents and losses are higher.  Thinner insulation also increases the positive-sequence resistance because there is more coupling between the phase conductor and the shield and shield currents are higher.  If the 132 kV cable has single-point grounded or cross-bonded shields, there will be no shield losses and the positive-sequence resistance will be lower.

RE: Impedance of power cable

There are four basic factors that determine the resitance of the conductor.

-Material
-Length
-Cross sectional area
-Temperature

Basic formula is R=P(L/A)
R=Resistance
p=Resistivity
L=Length (ft)
A=Cross sectional area (CM)

Resistivity (p) for copper at 20C is 10.37.

As Length increases resistance is increased. As temperature is increased resistance is also increased. Greater cross sectional area (bigger wire), resistance is decreased.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources