starts per hour
5
starts per hour
starts per hour
My field is civil/hydraulic engineering. I am looking for advice on the frequency of motor starts for pump sets.
I have a series of irrigation pump stations which will run continuously for 9 months per year. The pumps are fixed speed and will cycle on and off. I need to size the pump sumps to limit the cycle time. Normally I would allow no more than 8 starts per day but I am being pressed to reduce the sump sizes. The client's electrical engineer is suggesting as many as 10 starts per hour. The client also wants a long design life and minimum maintenance which would not seem to be compatible with 10 starts per hour.
Motor sizes vary from 20 kW (27 hp) to 600 kW (800 hp). Motors are air cooled. Ambient temperature may be 40 c (105 f).
Brian
RE: starts per hour
Further to above - will the provision of soft start/stop allow more frequent starting?
cheers Brian
RE: starts per hour
Starts / hour ratings vary by manufacturewr. There are minimum ratings defined in NEMA Standard MG-1 but that only goes up to 250HP. Here is a link to the chart...
http://www.joliet-equipment.com/allowable_starts.htm
Above NEMA frames all bets are off, but each motor manufacturer should be able to tell you from the serial number. Be carefull, because I have run into large frame motors rated for 1 cold start plus one hot start PER DAY!!!
As to a soft starter increasing the starts / hour capability, this is widely debated. Some experts think not, since the reduction in current is coupled with an increase in acceleration time and the net effect is null. Some beleive that the increased time allows more dissipation through the cooling fans during the longer acceleration, as opposed to all the waste energy being pumped quickly into the motor. The concensus in this group over time seems to be that there is no appreciable net gain in starts/hour capability. I will say however that soft starters will definately make your entire pump last longer by reducing torque stresses that are mostly unnecessary in an irrigation application.
Quando Omni Flunkus Moritati
RE: starts per hour
Utilizing Electronic Soft Starting and/or VFD will increase allowable number of stops/start.
NEMA is best for small motors.
Larger motors consult motor manufacturers.
All subject to load WK^.
RE: starts per hour
VFD definitely makes the start easier.
To further jraef's comment... under condition of heavy load torque and low inertia, an improperly conceived soft start can make the start more severe.  Other cases as discussed may have no effect or some improvement.
One thing to control in addition to the total number of starts per day or per hour (which limits long-term degradation) is the minimum off-time between starts.  It is tabulatdd in the link above.   If that limit is violated by starting a motor several times in quick succession without allowing cooling the motor may fail in short order from this short-term abuse.
RE: starts per hour
Thanks for the very helpful responses - .
I am pumping from a sump to a tank so fixed speed pumps are not a problem. My original design was for 3 duty and 1 standby pump at each station with each pump limited to only 8 starts per day. This give a fairly sedate design and low energy consumption. The client has complained that the sump and tank volumes are too large and he wants to increase the number of starts. He also wants to reduce the number of pumps from 3 to 2. (in fact the sump and tank costs account for less than 1% of the project cost but he has a "bee in his bonnet" on this issue). He is proposing up to 10 starts per hour per pump.
Reducing from 3 to 2 pumps will increase the daily power consumption. Also I would also assume that very frequent starts and cycle times will also greatly increase the power consumption?.
brian
RE: starts per hour
I think in general the energy associated with frequent starting is very small.
Wear and tear on the equipment is usually the big issue.
RE: starts per hour
Hello BRIS,
jraef hit the nail squarely on its head. Only people who can advise you are the motor manufacturuers as the specifications will vary from one to the other. From your wording and you alias I would guess you are in Australia. If so, Nema standards won't mean much much to you, all the more reason to speak to the paople who build the motors.
It is doubtful that the addition of a soft starter would allow you to increase number of starts per hour as the I2t usually comes out about the same as that of DOL.
If you go the frequency/speed drive option then number of starts is not an issue becuase you would vary the speed to control the level in the holding tanks ie rather than use start/stop control.
Let us know if the pumps are submersibles. If so, there are other issues you will also need to concern yourself with.
GGOSS
RE: starts per hour
Actually I am a Brit in Lebanon working as a technical assistant, on an Arab Funded project. The problem with these sort of assignments is that you have to be expert in everything or you have to rely on local support staff. I don't have a lot of confidence in my local support staff, hence I welcome the advice from this forum.
The pumps will be horizontal end suction. The pump stations will be located in remote areas.  Maintenance standards will be low hence I need to keep everything as robust as possible.
I will follow your suggestions and will put my questions to a couple of potential pump and motor suppliers. Thanks for the advice - any additional advice is more than welcome.
brian
RE: starts per hour
Hello BRIS,
My appology for accusing you of being an Aussie!
No problems with the pumps.
Soft starters and variable frequency drives may cause you some heartache if the cabinets into which they are to be installed are located outdoors. If this is the case, you'll probably be best served by electro-mechanical starting methods either full or reduced voltage and you will most certainly need to confirm max number of starts per hour with the motor manufacturer.
If this is to be a indoor installation with max ambient temp not exceeding say 35C, variable speed control would eliminate the need for frequent starting/stopping and will produce energy savings. This option therefore presents some real advantages worth further consideration.
Hope the above helps.
GGOSS
RE: starts per hour
GGOSS
Thanks - I have been accused of worse than being an Aussie –but off hand. I just can't remember what it was
The cabinets are indoors - I expect ambient temperature will exceed 40 C and humidity will be high. If this is a problem with soft starters I will have to add a room with air conditioning.
regards brian
RE: starts per hour
Check with softstarter mfgr. There are limits as to how many starts/hour they can tolerate.
Because of this limitation... it is generally accepted that softstarters do not significantly increase the number of permissible starts per hour.
Conversation with BOTH motor mfgr (regardless of motor rating) and softstarter mfgr. is advised. Afterall, wouldn't you expect them to be the definitive authority on number of permissible starts per hour.
Consider that in sizing motors for pumping applications, mtr. mfgr. takes into account the starting duty and sizes motor accordingly. Motor capability must meet the application requirements.
Other factors include time-between-starts, which allow heat from starting to be dissipated and rms load while running as a percentage of rated.
So check with manufacturer is a good idea and the definitive word as to the allowable limits.
ElectricPete's suggestion of VFD is a good solution as it eliminates concern over thermal stress from frequent starts....and ..... an added benefit....reduces mechanical stress to pumps.... VFDs = kinder gentler start & stop.
Additionally, with VFDs, you may be able to improve overall efficiency of operation by using variable speed capability and removing energy wasting throttling valves.
jO
RE: starts per hour
When I started in the water industry 30 years ago I was instructed to avoid variable speed at all costs and I have stuck rigidly to this policy ever since. I am now wondering that maybe you electrical guys have made some progress over the last 50 years and perhaps VFD is now a viable option.
The responses are leading me to now consider using variable speed. This will greatly simplify the system hydraulic operation and the civil works.
Before I start pursuing manufacturers I would appreciate some further advice:
1) Is there likely to be a significant cost difference between soft start and stop and VFD.
2) Given that the pump stations are in remote areas (in the Bekka valley in Lebanon) and the standards of maintenance and maintenance skills are poor, is there any significant disadvantage in using VFD instead of fixed speed with soft start and stop.
Cheers (Don't call me a Ludite) Brian
RE: starts per hour
Hello BRIS,
Pleased to learn this will be an indoor installation. You should note however when we refer to ambient temperature we are in fact referring to the temperature of the air flowing over the heatsink assembly of the soft starter or variable speed drive. As this is often higher than the external ambient, a review of equipment specifications/discussion with potential suppliers is suggested.
Variable speed will be significantly more expensive than start/stop control however the cost differential (and more) will be recovered over time through energy savings.
My only reason for not pushing the variable speed (or soft starter) technology harder here is because of your expressed concerns re the "standards of maintenance and maintenance skills". Your first experience needs to be a positive one, and unfortunately it would appear that cannot be guaranteed here.
GGOSS
RE: starts per hour
bris:
I would have to agree with GGOSS that in your situation, maintenance is the key factor and VFD's will probably not fit in this duty very well.
I am a bit confused though...I don't see enough information in your posts to determine that there will be an energy savings through the use of VFD's....I agree with electricpete that they will save wear and tear on the pumps, but primarily on starting...operation across the line if the pump hydraulics are designed correctly will work fine...I think we need to know more about the discharge of the flow to determine potential energy savings of the VFD's.
BobPE
RE: starts per hour
Bob
I have long transmission lines supply water from a surface water impounding reservoir to irrigation tanks. The irrigation demand varies from zero in winter to a peak in June and then back to zero.
The pumps are basically booster pumps located at points on the pipeline.  We are providing upstream break pressure tanks.
When I am pumping say 70% flow in August, with two fixed speed pumps, one will run continuously and the other will cycle on and off. Because of the long pipelines friction losses are high and when operating with two pumps I have maximum flow and maximum friction.
With VFD I would run the pumps continuously 24 hours per day and will therefore be pumping against a lower head and hence use less power.
As friction head is proportional to Q^2 and power is proportional to QH we use less power with 24 continuous operation rather than cycling between 50+ percent  and 100 percent flow.
I would also save power if the pumps were to be installed as in line boosters, but we also have large variations in the supply head.
This is all good in theory but I now need to look closely at the system curves and find pumps that can operate efficiently over the large range of duty points.
Brian
RE: starts per hour
Hello JOmega & BobPE,
JOmega; In your post of August 11 you said "Check with softstarter mfgr. There are limits as to how many starts/hour they can tolerate."
This is valid however you should note soft starters are capable of sustaining any duty cycle if they are selected correctly. For example we have many installed that are doing upwards of 300 operations per hour.
Prior to IEC60947-4-2 the user's choices were limited to selecting a product from a brochure. This is no longer the case. Product users are able to specify required duty and manufacturers/suppliers are obliged to offer a product that 'fits'.
BobPE; The original system proposed by BRIS was on of start/stop control. In addition you will note a substantial number of starts per hour were required due to 'pit' size.
By installing a Variable Speed Drive into this application, one would vary the speed of the motor to control fluid volume in lieu of start/stop control. The fact that the motor will be operated at below speed, will generate energy savings.
GGOSS
GGOSS
RE: starts per hour
3600 per hour = One start every 12 seconds.
I'm no expert but that sounds like a very poorly engineered system to me.
RE: starts per hour
Sorry, I shouldn't have used the term poorly engineered... I don't know the circumstances of the application.
I would think that most systems have some way to avoid that type of cycling... like an accumulator or some other adjustment to the mechanical system.  But I guess there are a wide variety of applications.
One would think that even with a soft start the equipment will not last long.
RE: starts per hour
Application was a palletizer.
Not withstanding that, the point was soft starters can be rated to any level of starting duty required. The 'weakest link' is generally the motor.
GGOSS
RE: starts per hour
Hi GGOSS,
you said:
"This is valid however you should note soft starters are capable of sustaining any duty cycle if they are selected correctly. For example we have many installed that are doing upwards of 300 operations per hour."
Your point is well taken...with some reservation and that is the law of diminishing return.
Yes, the Soft Starter can be oversized to tolerate a higher number of starts per hour. For example, a 50 hp unit with a limit of six starts per hour or once every 10 minutes... could be oversized to say 200 HP ... and then you could start that 50 HP motor as often as you like.
But at what cost ?  and how many starts/hour can the 50 HP motor tolerate ?
Certainly the 50 HP Soft Starter is a less costly unit than the 200 HP unit. Agreed ?  And I'm sure you realize that you have to provide, at additional cost, motor branch circuit protection (O/L etc) for the motor because you cannot use the BCP in the oversized Soft Starter since it is sized for a much larger motor..... Agreed ?
Now, suppose that instead of a 200 HP Soft Starter, a VFD were to be used. It could be sized at 50 HP and be a lot less expensive to the user than the 200 HP Soft Starter.
And by not having to oversize the motor to accommodate the higher number of starts/hour, the user realizes additional cost savings.
That, GGOSS is what I mean by "the law of diminishing return".
But to your thought, no argument! It can be done.
The only question to be answered is the one of cost/benefit ratio.
Next, not being familiar with IEC60947-4-2, could you provide some amplification to your comment about mfgrs. having to supply product based upon user specified duty requirements. It would seem that the mfgrs. would be required to provide custom designed products above and beyond their standard designed catalog listed products.
Is this so ? From a manufacturing view point, that would be a nightmare.... It costs a lot of money to custom design product for every customer's individual application needs.
Hope you  can provide additional insight as I'm over budget this month on ordering specs.
Thanks. ..
  jO
RE: starts per hour
Hello JOmega,
Your points are well taken and in fact fully supported. I too firmly believe VFD's are a far better option in cases of high starts per hour.
For more information re soft starter ratings to IEC60947-4-2, please view my post of July 14, 2003 in Thread237-59356 "Ratings of Soft Starters". Needless to say, many other posts in that thread also provide very good information.
Should you require any additional information and/or clarification, please do not hesitate to ask.
GGGOSS
RE: starts per hour
GGOSS:
Much appreciated. That's one of the best threads I've seen in the forum.
By-the-by.... have you noticed that SS mfgrs are going to smaller footprint (sized) units by providing an auto-bypass that transfers the motor to the mains when the acceleration is over ? In this way, the SS serves only to accel (or decel) the motor.... and generates no heat in the devices while running in bypass.
I would expect that this technique will also increase the number of starts/hour when the recommended time between starts is observed. I believe that some have also increased the air flow thru the heatsink as well to improve the duty cycle.
Thanks again.
jO
RE: starts per hour
jOmega - I have heard (read not documented)that at least one VFD manufacturer does not like to see the load switched to ACL after motor is up to speed.  Complaint was front end bus could be damaged.
Anyone else about this?
PUMPDESIGNER
RE: starts per hour
BRIS;
I would suggest using outlet damping as a viable alternative in this situation.  It will save you dollars (just not as much as VFD) and is easily maintainable.
RE: starts per hour
Hello jOmega,
Many thanks for the kind words.
Soft starters with inbuilt bypass contactors and/or rated for use with external bypass contactors are also covered by the standard. A utilisation category (AC53b) has been established accordingly. However there are a few issues worth noting. As these are not relevant to this thread, I will start another (or write an FAQ) over the next couple of days.
GGOSS
RE: starts per hour
Thanks for the response.
What is outlet damping?
I have now modelled my hydraulic system and I am happy that fixed speed pumps with on off control work well. From a hydraulic/efficiency point of view there will be no advantage in using VFD. I have also got the maximum number of starts at no more than 3 times per hour.
This takes me back to my initial problem of number of starts per hour.
The comment that: “VFD's are a far better option in cases of high starts per hour" I understand to mean that VFD will be more robust than Soft start for frequent starts but from other posts I also read that VFD will be significantly more expensive. Maintenance (or lack of it is a key factor) hence I am taking the advice that VFD is not the solution.
So I think my solution is soft start. Although I now need to question why we are using soft start rather than simple Star Delta starting which must be both more robust and less expensive.
Brian
RE: starts per hour
Just to add my comments on the effect of the use of soft starters.
1. The use of a soft starter will not thermally increase the number of starts. This is because the power dissipated in the motor during start is a function of the full speed kinetic energy of the load plus an additional amount related to the time taken to overcome the work component of the load. This is the same for all means of starters. If the start torque is limited too much, the start gets extended excessivly and the power dissipated in the motor is increased.
2. The use of the soft starter will reduce the electrical disturbances on the supply and this may allow the starter to be operated more frequently.
3. The use of the soft starter will reduce the transient loading on the supply, and the mechanical shock loading on the motor and driven load. This will reduce the stresses on the machnine and can reduce the frequency of maintenance on the equipment.
To summarize, if the number of starts are restricted by the motor thermal rating, then the soft starter will not increase the number of starts per hour. If the starting frequency is limited by the disturbances on the electrical supply (Flicker regulations and the like) then the use of the soft starter may provide a useful gain. If the starting frequency is limited by the mechanical degradation at each start, then the soft starter will provide a useful extension of equipment life, or increase in start frequency.
Best regards,
Mark Empson
http://www.lmphotonics.com
RE: starts per hour
GGOSS:
Great. Will be watching for new thread or FAQ.
Kind regards,
jO
RE: starts per hour
PUMPDESIGNER
You Said.....
"I have heard (read not documented)that at least one VFD manufacturer does not like to see the load switched to ACL after motor is up to speed.  Complaint was front end bus could be damaged."
I'm not sure how the "front end" of the VFD gets damaged if the load is suddenly disconnected from it. To me, it would be no different than giving the VFD a STOP command that immediately turns-off the output IGBTs (Coast-to-Stop mode).
But I do know that there are VFDs that are not designed to tolerate the interruption of power flow from VFD to motor under load. There are transients that occur as the contactor between the VFD and the Motor opens...that can damage the output GBTs.
Some manufactures will allow opening the power flow to the motor under load, with the addition of 100 microHenries of inductance between the VFD output and the line side of the contactor. (or a 1-1/2% reactor with gapped core can also used).
There are a few manufacturers that claim they can tolerate the interruption of power flow; Danfoss VLT 4000, 5000,6000, & 8000 drives.... to mention one...In fact, while witness testing some 600 HP drives being factory tested about a year and a half ago... I observed that part of their test routine is to open the output between drive and motor.... and..... to reclose the motor on a running inverter without damage.  I was impressed.  I've seen other mfgrs. drives take a hit on such a test.
Ok.... them's the words on VFDs and interruption of output power flow to the motor ....i.e., taking the motor up to rated frequency and then disconnecting it from the VFD and transferring it to ACL in asynchronous fashion. There is however a concern about how much current the motor will draw when it is closed in on the line power...remember the rotating field inside the motor isn't synchronized to the line before the transfer.... ergo....aysnchronous....
Usually there's a timer....that gives a bit of time before the motor is closed in to the line power... and in this way, allows the flux field in the motor to decay before closing in.
Now to the case of the SoftStarter.... This is a different case...
Consider that the bypass contactor is a three-pole contactor, the contacts of which short across each inverse-parallel set of SCRs.... In this way, the field in the motor is synchronized to the line because it was directly supplied from the line thru the SCRs while soft starting.
No change to phase sequence occurs.
With no current flowing thru the SCRs.... they cease to conduct. If they don't conduct.... no power thru them...ergo...no heat ....
So, using a bypass contactor to connect the motor to the line IS different for a VFD than it is for a soft starter.
Ok ?
jO
RE: starts per hour
jOmega - Thank you for your considered response to my question.  I saved the file, will quote you from now on.
Just kidding.
Thought you were correct on everything you stated.
PUMPDESIGNER
RE: starts per hour
BRIS:
Your comments:
"The comment that: “VFD's are a far better option in cases of high starts per hour" I understand to mean that VFD will be more robust than Soft start for frequent starts but from other posts I also read that VFD will be significantly more expensive. Maintenance (or lack of it is a key factor) hence I am taking the advice that VFD is not the solution."
1. The advantage of using a VFD when you have a high duty cycle (frequent start-stop sequence per hour] is not because of the robustness of the VFD.
2. The advantage is that motor and pump are not subjected to anywheres near the stress (both electrical and mechanical) that DOL or Softstarting imparts to the motor and pump.
3. Consider that if you set the current limit on the VFD to 100% ... that the motor can start and accelerate at 100% current as often as you like, all day, all week, all year, and not exceed its thermal design rating.
4. In addition, the pump is not subjected to the shock starting torque that DOL or Softstarting subjects it to.
Now, wouldn't you say that that was much friendlier to both the motor, and the pump ?
As to the argument of cost differential, it's a one-time cost and in addition, there can be energy savings realized with it as well.
Balance this against the cost of recurring maintenance, reduced life of pump and motor, and downtime.
Still think the VFD is more expensive ?  long term ?????
RE: starts per hour
Jomega
Thanks for the clear arguments
VFD will also be friendlier to the pipelines which are likely to be fibreglass (GRP) and will be weakened by fatigue caused by hydraulic transients from frequent starting.
BUT, the pump stations are in a undeveloped region where maintenance skills are basically blacksmith technology and limited to little more than swinging a big hammer.
What I see in existing pump stations is cabinet doors permanently open, automatic trips by-passed, instrumentation disconnected etc. (replacing fuses with 6 inch nails is a real possibility). Supply voltage fluctuations vary from 13 to 16 kv.  Robustness in my situation means it has to be robust against unskilled and ham fisted operators and maintenance personnel. The staff do manage to keep  basic technology working, in a fashion, but rarely as the original design engineer intended.
Hence my concern over VFD - I think I should also be concerned over soft start?
Brian
RE: starts per hour
BRIS,
Even with all the fascinating and well thought material above, I don't see what I consider to be a very important point addressed. You mentioned early on that you were going from a 3 pump system to a 2 pump system, hence the need for more starts/hr. There is a flaw in the concept that perhaps your client is missing. No Redundancy. If you have "blacksmith technology" skill levels in the maintenance people, wouldn't it benefit the owner to make sure the system has a modicum of backup capacity? I would think that in your corner of the world, reliability of irrigation water is critical (not that it isn't everywhere actually). Prudent design theory would have a system wherein 2 pumps can carry the entire load, but 3 are installed and alternated for even wear-and-tear. That way the system can still operate fully when one pump is down for "big hammer" maintenance. My first approach would be to sell the old design concept back to the client. Ppoint out the losses that will occurr when (not if) one pump dies at a critical time. We all know that it WILL happen.
As to SS vs VFD, I can offer my 2 cents worth as well. We sell RVSS starters to the portable rock crushing industry all over N. America and there are no electricians at the sites for maintenance. Just "Bubba" the crusher operator who is a step up from ditch digger. RVSSs work fine in that environ, and reliability is such that they rarely need to open the box and look oinside, thus avoiding trouble.
Although VFDs are used successfully in that industry as well, your concerns are valid not only for maintenance but also for their being a focal point for curiosity. More often than not the problems I must solve in the field with VFDs at sites with unsophisticated operators are due to someone "tweaking" the settings because they THINK they know what they are doing. It can be a real nightmare.
By the way, the reason VFDs can start the motor more often than RVSS has nothing to do with robustness (robustosity?). It is simply because the motor can be accelerated to full speed without exceeding FLA because of the ability to alter frequency. Less heat at acceleration = more thermal capacity remaining in the motor = more starts/hr. If anything, the additional components required to accomplish this would decrease the "robustosity" as comparison to the RVSS.
Good luck.
RE: starts per hour
Bris:
I understand well your concern about shock to the piping that is attributed with both DOL starting and stopping. While SoftStarters can mimimize the shock somewhat, it is far more gentler to utilize a VFD with a "Pipe Fill" mode that controls the fill rate of the pipe as a function of pressure build and with -up...
Several VFD manufactures have incorporated such control in their designs for the water industry.  I know the Danfoss VLT 8000 has it and a New Zealand VFD manufacture (PDL) I believe also has it. I wouldn't be surprised if Grundfos also has it.
As to the "tweaking" problem, many drive manufacturers have removable keypads capability which elimiates the tweaking. Some VFDs also have a Lock-out mode so that parameter adjustment requires a password be entered before gaining access to the parameter adjustment capability.
Also, consider that with "communications" capability and proper software, the drive can be set-up with a lap-top computer interfaced to the VFD. This then impedes the "tweaking" by those that have nothing better to do than to push buttons and twist knobs.... and the Base Setup parameters can be maintained on the hard drive of the Laptop... as well as copies of the set-up after adjustment... etc.
And don't overlook the fact that Soft Starters are very "tweakable" too...
Pipe Fill Mode functions to eliminate the "hammer" that occurs on both starting and stopping the pump by controlling the pressure build-up and build down so as to prevent "shock" occurrences.
jOmega