LPG - Vacuum Breaker Requirement for Pressurized Vessel

LPG - Vacuum Breaker Requirement for Pressurized Vessel

LPG - Vacuum Breaker Requirement for Pressurized Vessel

(OP)
Does an LPG (Butanes) Pressurized Storage Sphere require a vacuum breaker?  Our existing tanks were designed with a vacuum pressure (actually a duo-check valve) that is set to open at 1" H2O and has a design pressure of 90 psi (tank design pressure) at ambient conditions.  I have been unable to locate a vendor that can provide a vacuum breaker that can meet our specs.  Can you help me?

RE: LPG - Vacuum Breaker Requirement for Pressurized Vessel

msavila,

Do you have an ASME vessel with a code dataplate ? If not, do you have a mfr's print with the National Board number on it ? For a few bucks, the people in Columbus OH will send to you the design data submitted to them at the time that the vessel was built...

If you can read the dataplate, you may find the vacuum rating on it....remember "FV" means "full vacuum protection/

What are the dimensions of your vessel ? If the diameter is 6 feet or less and the heads are dished, and the design pressure is 90 psig, the chances are good that you have far more than a 1" H2o vacuum rating.

Just my thoughts....

MJC

RE: LPG - Vacuum Breaker Requirement for Pressurized Vessel

msavila (Chemical):

Mike Cronin is giving you some great, basic and essential advice that should go in your hip pocket for when you're dealing with tanks and pressure vessels.

You ask if a vacuum breaker is required for Butane storage.  Again, this is a basic and elementary need that is easily resolved if you revert back to your Thermodynamics and physical properties studies.  If the tank is going to be dedicated solely to Butane storage (saturated), then you need to refer to the vapor pressure of Butane:

Temp, oF  Press, psia
14.000      10.119
16.000      10.590
18.000      11.078
20.000      11.584
22.000      12.107
24.000      12.649
26.000      13.210
28.000      13.790
30.000      14.390
32.000      15.010

Depending on your tank's location and elevation, the above table should tell you if you're going to generate a vacuum by allowing the tank's contents to cool down with atmospheric winter conditions.  If you're located in Kingston, Jamaica, Port of Spain, Trinidad or Pucallpa, Peru I wouldn't worry about needing a vacuum breaker in a butane tank.  If you're in the North Slope, you'd better have one.

Normally, I would expect to find the tank has been FV'd and I would not rest until I had the documentation that Mike Cronin lists - especially the fabrication drawings.  You need these for inspection and as reference for all tank-related calculations (such as the vacuum breaker).

Art Montemayor
Spring, TX

RE: LPG - Vacuum Breaker Requirement for Pressurized Vessel

(OP)
Hello MJCronin & Montemayor,

Thank you both for your replies to my post.  I was able to dig up the fabrication drawings in our drawing room.  The vessel was built in 1969 by Chicago Bridge & Iron Company (CB&I), and the tank was rated for -12.55 psig vacuum.  It is 62 ft in diameter, 90 psi MAWP, 135 psi test pressure, with top thickness of 1.044" and bottom at 1 3/16".

I performed several calculations using the most extreme operating conditions and worst case scenarios under our current operation, and have determined that we cannot exceed the -12.55 psi vacuum rating of the sphere.  I have reviewed them with our process engineering group here and submitted an MOC to remove the vacuum breakers (check valves) from the sphere all together.

I appreciate your input and look forward to any other comments or suggestions you may have.

Thanks Again,

Mark Avila
Operations Engineer
Los Angeles Refinery
ConocoPhillips

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources