UL 142

UL 142

(OP)
I have a question -- we have a UL 142 tank which we will need to put a vacuum releif on and wanted to know if the standard allows these tanks any vacuum rating whatsoever .  If none, then how does one put a vacuum relef on such a tank.....

RE: UL 142

I beleive the manufacture will provide some type of rating for vacuum pressure. I think the best thing to do is call them and get their rating information or suggestions for appropriate valves.

Christopher Caserta
ccaserta@us.tuv.com
Ph:904-225-0360

RE: UL 142

Along the same lines as the original post in this thread, I'm having to validate the vent systems (2" and 6") on a 1500 gallon, horizontal UL-142 tank used for diesel storage.  Unfortunately, that seems to be the only information that I can find in relation to the existing installation, no manufacturer, no design pressures, no venting requirements marked on the tank.

The vent sizes seem appropriate per the tables in UL-142 except the 2" vent has a flame arrestor elevated some distance above the tank and I wanted to look closer at the inbreathing design.

Looking at the Glossary section for UL-142, they indicate certain definitions that apply for the purpose of the standard including

3.2 ATMOSPHERIC TANK – A storage tank that has been designed to operate at pressures from -0.5 psig (-3.4 kPa) through 1.0 psig (6.8 kPa) measured at the top of the tank.

From the above language, could one conclude that an atmospheric tank built to UL-142 would have at least a rating of -0.5 psig and 1.0 psig as an indication of its external and internal MAWP?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources