Hello Everyone!
How can I calculate the single phased short circuit current on the primary side of a Yd-connected transformer?
I know that a Dy-connected transformer single phase short circuit turns into a two phased current, but what about the other way around???

RE: short circuit calculation

I'm not quite sure what your question is. . . .

The available fault current on the primary side would be determined by the upstream system.

Unless. . . are you're concerned about motors on the secondary side backfeeding into the primary side through the transformer?

RE: short circuit calculation

Suggestion: The upstream power distribution system must be known to calculate faults on the transformer primary. The contributions from downstream may be considered; however, they are often neglected since they will be small, i.e. substantially reduced by the transformer impedance.

RE: short circuit calculation

(OP)
Let me clarify a little.

I have a grid consisting of the utility which has a grounded network. I am a consumer with a Dy-connected transformer with a generator connected to the secondary side. I there is a single phase short circuit on the high voltage side what would the contribution the fault be from my generator??

RE: short circuit calculation

It will be zero after the utility breaker opens to clear the fault.  While there is a utility source, there will be positive- and negative- sequence currents in the secondary.  Protection for Unexpected Delta Sources, Ken Behrendt, SEL, has sequence diagrams that will help in calculating the fault contribution from you generator.  http://www.selinc.com/techpprs/6143.pdf

RE: short circuit calculation

Your generator will contribute positive and negative sequence fault current, as the zero sequence is blocked. This contribution will be limited by the transformer impedance, as jbartos suggests and it's unlikely to be the utility's main concern. They will be more interested in assuring that energization of their de-energized line is prevented during maintenance, for personnel safety. In any event, these are matters that should be addressed jointly with the electric utility.

RE: short circuit calculation

See Thread238-47990. It has the correct answers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources