Fuel savings

Fuel savings

Fuel savings

(OP)
We have two Cleaver Brooks fire tube boilers. We have a CB400-600 and a CB 657-350. The 600hp can run on gas or oil, the 350hp can only run on oil. Do to productin requierments we use only one boiler, we prefer to run on gas so we use the 600hp. We are thinking of converting the 350hp to gas. My question is, does a small boiler use less gas than a larger one to make the same amount of steam? Thank You; Bill

RE: Fuel savings

carlstadt, yes and no. A 600 hp CB will have a different radiation loss than a 350 hp CB boiler but this should be of little concern. The big factor is your load. A firetube boilers operate at higher efficiencies at higher firing rates (generally.) So, if you have a 275 hp load, the 350 hp CB, operating at a higher firing rate, will meet the load more efficiently than the 600hp CB operating at the lower end of its firing rate.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources