Thermal expansion of glycol mixture
I need the coefficient of thermal expansion for a 50% mixture of ethylene or propylene glycol in water from 20 to 95C. I have found values for 100% glycol (650 to 700E-6 per degree C), and water is about 200E-6. Would it be correct to average the values for 100% water and 100% glycol?
RE: Thermal expansion of glycol mixture
http://www.mrc-eng.com/Downloads/Brine%20Properties.pdf
but please review also FAQ731-376 point 2!
prex
http://www.xcalcs.com
Online tools for structural design
Thank you. I did search on the Internet quite a bit but under "thermal expansion" and "glycol", and didn't think to try "brine".
I'm still missing something, though. Several sources list the volume coefficient of thermal expansion (Beta) for water at 20C as 0.000207 per degree C. Looking at the chart in your reference, for 0% concentration, the chart shows 0.055 per degree K.
Would you please help me reconcile these numbers? Thanks.
I suggest that you contact the people at DOW Chemical....
They supply a number of different grades of both ethylene and propylene glycol under the "DOWFROST and "DOWTHERM" brand names
Good luck
MJC
I spent a long time talking with a pharmaceutical engineer about controlling his brine concentration and i was doing well till i asked if it was a sodium chloride brine. He looked at me as if i was from another planet and patiently explained that it was monoethylene-glycol and water. Well, what else could it be?
Beware of all such euphemisms!
I too might have reciprocated in the same way. But you didn't talk to me definitely
As it is mostly used for chilling application, increase in concentration is not a problem. It gets diluted often because of mixing with cooling water (in Bulk API plants)
http://www.houghtonchemical.com/fluids/wintrex/