BENZENE LINE - UNCLASSIFIED HAZARDOUS ZONE

BENZENE LINE - UNCLASSIFIED HAZARDOUS ZONE

BENZENE LINE - UNCLASSIFIED HAZARDOUS ZONE

(OP)
The idea was to install explosion-proof electrical rack, for small power distribution (with min.C.B.'s or fuses) close to the existing benzene line ( distance, d=15 feet )and new benzene line (distance, d1=21 feet).
Now customer want unclassified electrical panel,( non explosion-proof) explaining that we are outside explosive zone. Please, your comments.

RE: BENZENE LINE - UNCLASSIFIED HAZARDOUS ZONE

Your client is right, if there is the pipe is fully welded and in a well ventilated area without containment.  Don't like the idea myself, but that's what the code say.  Area classification is based on normal operating conditions and not based on accidental event.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources