Connecting multiple DH+

Connecting multiple DH+

Connecting multiple DH+

(OP)
I have 5 / PLC5 approx 400ft from control-room where there is a single SLC.  I want to add an HMI (1784-PKTX).  Can all the DH+ be connected in the control-room in a "star" configuration without significant loss of data speed?  Thanks

RE: Connecting multiple DH+

Please refer to Allen Bradley manuals, concerning how to make your connections for DH+. Unless it has changed, I understood it as having to daisy-chain, from one device to the other. So, from the PKTX to the SLC or the first PLC5, then the next and so forth. At one of our mainline stations, where we have three pipelines systems, I have three PLC5, 1784-KE(connected to a radio, for communications to a Micrologix 1000), and a KTX(D). The KTX(D) allows PLC programming and communications for the HMI.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources