Storage temperature for Furnace Oil

Storage temperature for Furnace Oil

Storage temperature for Furnace Oil

(OP)
Is there a requirement that the storage temperature of furnace oil tank be maintained below flash point if the tank is not blanketed with Nitrogen.

regards

sgoel

RE: Storage temperature for Furnace Oil

There is no such rule. But then the area where you are storing furnace oil comes under Hazardous Area classification. The Petroleum Act, 1934/The Petroleum Riles, 1976 provides some regulations, if you are maintaining the temperature of Class C petroleum (which furnace oil is)above its flash point. I will put here some of the rules.

Petroleum Class C: Means petroleum having a flash point of 65 deg C and above but below 93 deg C

Rule103: Hazardous area
ii) petroleum or any inflammable liquid having flash point above 65 deg C is likely to be refined, blended, handled or stored at or above its flash point.

Rule 104: Classification of hazardous area
A hazardous area shall be deemed to be -
- a division 0 area, if inflammable gases or vapors are expected to be continuously present in the area.

- a division 1 area, if inflammable gases or vapors are likely to be present in the area under normal operating condition if inflammable gases or vapors are likely to be present in the area only under abnormal operating conditions of failure or rupture of an equipment.

- a division 2 area, if inflammable gases or vapours likely to be present in the area only under abnormal operating conditions of failure or rupture of an equipment.

Now the area where you store the oil should comply with the rules and regulations of hazardous area and should be approved by Chief Controller of Explosives (CCE).

I suggest you to contact any Competent Person of CCE.

One more thing is considering the ambient conditions in India, it will be ok if you maintain 500C for storage and higher temperatures for pumping. This is my general practice and never had problems. Unnecessary heating would leave you with energy losses.

Note: I presume you are not an NRI (The rules are applicable only in India)

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources