increasing flow will decrease AHU capacity?

increasing flow will decrease AHU capacity?

increasing flow will decrease AHU capacity?

(OP)
is that true?
increasing water flow for high value will decreases the AHU capacity?Why?

thanks.

RE: increasing flow will decrease AHU capacity?

Water coil Heat transfer coefficient increases with water flow.
Heat transfer rate (water to air) is directly proportional to the product of water flow rate and water temp rise through water coil.
This means the AHU water coil has a larger capacity with increased water flow rate.



RE: increasing flow will decrease AHU capacity?

I agree with more water equals more AHU capacity, but with the faster flow a lower DT (Delta Temp) is produced a crossed the coil. If the chiller is designed with X GPM at Y DT and BTU = GPM * DT then lower DT equals lower capacity.

RE: increasing flow will decrease AHU capacity?

To Macbeth
I have to disagree with your theory.
Lower DT means constant "capacity" with increased GPM across the coil. Actually you refer to constant prevailing "load" and not to increased potential "capacity".
With DESIGN heat load and increased GPM (beyond design value), DT will decrease compared to designed DT, but chiller LOAD will not change (capacity will increase a bit due to better heat transfer coefficient).
But coil increased capacity means that it can absorb larger heat load, keeping DT at design value.
Copressor load will be the problem: it may not be able to handle the increased capacity, impose lower DT and force the system to balance at a new working point (pressures, temperatures and capacity).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources