(OP)
I'm working on a floor system below a bank vault.  What have others used for live loads is such a situation?  Perhaps the 250 psf required for heavy storage in the IBC?

RE: Bank Vault Loads

Recently designed a headquarters bank.  The vault was on first floor (above the basment).  The vault walls, doors, and ceiling were supplied by a vault company.  The walls and ceiling were precast concrete.  The general contractor provided the floor which consisted of a 12" thick concrete slab with (3) layers of bars in both directions.  The bars were off-set four inches.  The reinforcing was set this way for security reasons.  Embed plates were provide at the perimeter for securing the walls of the vault.  This vault was going to have safety deposit boxes all the way around the vault.  I checked the vault floor based on the actual dead load of the boxes, loaded weight of the boxes and an additional live load (as well as the dead load of the concrete).  The additional live load may be very conservative but my boss insisted on extra capacity because the future use may change or heavier equipment may be put in the vault.

RE: Bank Vault Loads

Maybe they should put some ductile iron pipe filled with high density concrete in the floor too.

RE: Bank Vault Loads

I'd say 250 psf sounds appropriate.
I was involved with a bank vault demolition, and it was 18 inches thick (all 6 sides) with 3 layers of #5 bars at 4" o.c..  The demolition contractor was not too happy.
From what I understand, the rebars at 4" o.c. are so that a) you cant 'blow up' the vault, and b) if you could, you'd never get your hands through the twisted rebar mess remaining.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources