Recommended ventilation rate
Recommended ventilation rate
(OP)
Does anyone know the recommended ventilation rate for a photocopier room, per photocopier? Specifically I am working on a room that is 8ft x 12ft with a 9ft ceiling; one photocopier, one occupant.
Based on one occupant, recommended office ventilation is 20 cfm, but photocopiers generate ozone (at what rate I'm not sure). I was thinking that 6-7 ACH (86-100 cfm) would be more than adequate, but would appreciate anyone's thoughts.
Based on one occupant, recommended office ventilation is 20 cfm, but photocopiers generate ozone (at what rate I'm not sure). I was thinking that 6-7 ACH (86-100 cfm) would be more than adequate, but would appreciate anyone's thoughts.





RE: Recommended ventilation rate
I think you would not worry about putting more ventilation if the photcopier is a new type. The older models exhumed fumes and needed some ventilation (exhaust over the photcopier). The new ones just are an added heat load in the room. 20cfm for a person is good for ventilation.
But if your total heat load is higher than a similar room without a photocopier, you will have to supply more air to satisfy the load. MOre supply air to come from the central AC unit. Since the outdoor air intake is set up at the unit itself, you will get more ventilation in that room anyways.
Vic
RE: Recommended ventilation rate
Thank-you for your response. The photocopier is a new type, but there are other issues. I'm not designing the room; I'm rebalancing the building exhaust system. The room is in an old government office, and the woman who uses the photocopier heard that the ozone it generated was going to kill her. She made a huge complaint and a new exhaust fan was installed to exhaust from the space.
The problem was that rather than using a new exhaust duct the contractor tapped into the existing washroom exhaust system. This had the result of 'robbing' exhaust from every floor below. At the same time my company was hired to design the upgrade for their washroom exhaust system, which we did, but we were never informed of the new fan. Now I'm trying to find a number that I can throw at the building manager to keep the photocopier lady happy, and allow the washrooms to exhaust.
Chris
RE: Recommended ventilation rate
RE: Recommended ventilation rate
Why even write? Just trying to get your 'reply' numbers up?
RE: Recommended ventilation rate
Results
http://a1851.g.akamaitech.net/f/1851/2996/24h/cache.xerox.com/downloads/usa/en/e/ehs_safetyfacts.pdf
http://a1851.g.akamaitech.net/f/1851/2996/24h/cache.xerox.com/downloads/usa/en/e/ehs_ozone.pdf (this link takes a little bit more time)
Xerox Corporation claims, with 1 fresh ACPH the ozone is well within the limits.
Hope this helps.