Outdoor detection recommendation

Outdoor detection recommendation

Outdoor detection recommendation

(OP)
Does anyone have a recommendation for fire detection required for elevator lobbies when elevator doors open to outside covered spaces?

This is a multi-unit, 3-story residential type building with elevators opening only to the outside. NFPA 72 Appendix A item A6.15.3.5 indicates that smoke detectors should not be installed outside. But it references 6.15.3.7, which notes that if ambient conditions prohibit smoke detector installation, other automatic detection is permitted.

Should we use heat detectors? Other thoughts?

RE: Outdoor detection recommendation

I don't have an answer for you.

But the whole idea of elevator recall seems like it was intended for indoor installations -- would you really be protecting against an elevator opening onto a fire outside a building?  Is there anything flamable out there?

I'd suggest calling your AHJ and see what he thinks.  Put in whatever he wants.

RE: Outdoor detection recommendation

Alternative flame detection equipment could include flame detectors as manufactured by MSA, Detronics, and Thorn.

The principles involve include UV/IR flame detection and are regularly used in the oil and gas business.

Although I am not overly familar with NFPA, if you contact companies like above they should be able to provide you direction as to whether their equipment meets the regulations.

RE: Outdoor detection recommendation

From what I heard at the Spring NFPA meeting, I suspect the AHJ will agree to heat detectors.  

RE: Outdoor detection recommendation

Beam type smoke detectors are available with a much wider operating temperature range than the temperature range of spot type detectors.

RE: Outdoor detection recommendation

Beam detectors won't work too well in sunlight, though.

RE: Outdoor detection recommendation

people, we should be careful with what we install. what i know is that the conventional heat and smoke detectors are passive components which depend on the migration of heat/smoke to the detector.as such, having them outdoor where there may be draft will render them useless for heat/smoke detection purposes. I will go with the flame detector, which is active.
regards

RE: Outdoor detection recommendation

Careful with the flame detector, make sure you have one that won't false trip on direct or reflected sunlight.

RE: Outdoor detection recommendation

I have this same problem here and I talked to the Elevator inspector on this issue and he said there is no requirement in open air lobbys, but if it came to an issue to use pull stations to recall elevator but did not make much since, He also stated you may want any alarm to recall elevator, but then was left up to AHJ.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources