Positive Pressure Ventilation for Electrical Rooms
Positive Pressure Ventilation for Electrical Rooms
(OP)
Can someone give me some guidance and resources on how to design a positive pressure ventilation system (not airconditioning) for an electrical room. Things I'm looking for:
1. How much pressure is required to successfully keep out dust?
2. Types of filters available and allowable velocities through the filters.
3. Are inlet and outlet fans needed or can a fan blowing into the room alone be sufficient?
Thanks.
1. How much pressure is required to successfully keep out dust?
2. Types of filters available and allowable velocities through the filters.
3. Are inlet and outlet fans needed or can a fan blowing into the room alone be sufficient?
Thanks.
RE: Positive Pressure Ventilation for Electrical Rooms
To secure a copy of ASHRAE Standard 62-2001 or any of the other ASHRAE documents referenced in this guide, contact:
American Society of Heating, Refrigerating and
Air-Conditioning Engineers, Inc.
1791 Tullie Circle NE
Atlanta, GA 30329
Phone 1-800-527-4723 — publication orders only
Phone 404-636-8400 — technical inquiries
Fax 404-321-5478
Web www.ashrae.org
Ventilation Rate Procedure (Section 6.1) presents "...one way to achieve acceptable indoor air quality", namely, supplying each occupied space with ventilation air of specific quality and quantity. Outdoor air is used to dilute anticipated contaminants to acceptable concentration levels.
In contrast, the Indoor Air Quality Procedure (6.2) presents "...an alternative performance method...for achieving acceptable air quality" by quantitatively describing acceptable indoor air quality. It sets limits on the concentration of known and specifiable contaminants in an effort to achieve acceptable indoor air quality in the occupied zone in a more direct way that the Ventilation Rate Procedure. More specifically, the Indoor Air Quality Procedure sets concentration limits for 10 contaminants, prescribes subjective analysis to determine acceptable odor levels, and describes the use of treated recirculated air to reduce the minimum outdoor airflow rates presented in the standard
Your internal pressure must over come external wind pressure.
Inlet fans can be used for pressurized rooms
Also refer too NFPA 90A
http://hfpa.otsg.amedd.army.mil/refs/1191/MH1191_20020702_08_HVAC.pdf