(OP)
It is my understanding that Line-to-Ground faults can occurr on a Delta bus if you have a zig-zag grounding transformer connected to this bus.  Is this correct?

RE: Zig-Zag on Delta Bus

A Zig-Zag grounding transformer provides a consistent potential to ground for each phase. Since there is a potential to ground, a ground fault can occur. Because of the inherent design of the Zig-Zag system, however, the GF current is usually limited because it must flow through two windings of the transformer system.

RE: Zig-Zag on Delta Bus

Normally, when you have a delta distribution system, you usually grounded through a zizg zag transformer.
The transformer provides a path to ground for any ground fault in the system; allowing the ground relay to trip for this fault, otherwise the relays will operate until you have a double fault.
I installed a delta 15 KV distribution system in Cameroon and this was the way they usually did it.
I must confess most of my experience is with so called "american" systems where all the distribution systems are grounded star.

RE: Zig-Zag on Delta Bus


gabi:  "Results 1 - 10 of about 1,800. Search took 0.16 seconds"
  

RE: Zig-Zag on Delta Bus

Suggestion: Visit
http://www.powerohm.com/catalog/NGCAT00.pdf
etc. for more info on zigzag transformer
The grounding zigzag transformers are usually rated for 10Second, 100% insulation level
This needs to have the upstream protector tripped within 10seconds, else the transformer may be permanently damaged.
The non-triplen harmonics will flow through the zigzag to the ground. Now, it depends on how the primary of transformer with delta secondary is system grounded. If there is a wye winding with solidly grounded neutral system grounding, then the zigzag transformer will experience more stable voltage in comparison with the wye connected primary without a solidly grounded neutral system grounding.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources