It is my understanding that Line-to-Ground faults can occurr on a Delta bus if you have a zig-zag grounding transformer connected to this bus. Is this correct?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Zig-Zag on Delta Bus
RE: Zig-Zag on Delta Bus
The transformer provides a path to ground for any ground fault in the system; allowing the ground relay to trip for this fault, otherwise the relays will operate until you have a double fault.
I installed a delta 15 KV distribution system in Cameroon and this was the way they usually did it.
I must confess most of my experience is with so called "american" systems where all the distribution systems are grounded star.
RE: Zig-Zag on Delta Bus
gabi: "Results 1 - 10 of about 1,800. Search took 0.16 seconds"
RE: Zig-Zag on Delta Bus
http://www.powerohm.com/catalog/NGCAT00.pdf
etc. for more info on zigzag transformer
The grounding zigzag transformers are usually rated for 10Second, 100% insulation level
This needs to have the upstream protector tripped within 10seconds, else the transformer may be permanently damaged.
The non-triplen harmonics will flow through the zigzag to the ground. Now, it depends on how the primary of transformer with delta secondary is system grounded. If there is a wye winding with solidly grounded neutral system grounding, then the zigzag transformer will experience more stable voltage in comparison with the wye connected primary without a solidly grounded neutral system grounding.