If a two prong plug (one prong is polarized) is plugged into a three prong receptacle is the appliance with the two prong plug "grounded"? I have a metal box fan with a flat two-wire cord with a two prong plug. When I take a volt pen and touch the cord in several places the volt pen has a steady glow. When I touch the metal part of the fan with the volt pen it does not glow. Now when i turn the fan on and touch the metal part with the volt pen it glows steady. This tells me the fan is not grounded. Is this correct. Should the fan be disposed of?





RE: Two Prong Plug
RE: Two Prong Plug
Best Regards
Ray Micallef, P. Eng.
Power Generation/Utility Industry
RE: Two Prong Plug
RE: Two Prong Plug
If your "Glow Pen" is like all that I have ever used it is very inaccurate in picking up accutate indications of voltage or amps. It will pick up all kinds of stray voltage including static. Would never use it to detect elect if my life depended on it. Good for continuity i.e. chek fuses, some types of light bulbs, conductor integrity etc.
If you are terribly concerned get a multimeter set it for volts AC and check for actual voltage. If it is an older fan I would re-wire and attach a ground or better yet get a new fan --- not very expensive and it would resolve your issue with the one you have.
Good Luck
ietech
RE: Two Prong Plug
RE: Two Prong Plug
You are correct, I think that is the reason for the original post.
This is simply resolved by adding a three wire cord and three prong plug, then grounding the fan chassis to the ground wire.---- OR buy a safe fan.
If "Safe" has polorized plug on his fan it is most likely a double insulated unit and does not require a ground.
His test equipment "Glow Pen" is questionable also. Most of these types will show voltage if you touch it with your finger or even static in the air.