Three phase autotransformer
2

Three phase autotransformer

Three phase autotransformer

(OP)
What problems can arise if I use a three phase autotransformer with a center tapped delta power source? Sinse each phase is 240 Volts, I am told the one tapped phase will cause my autotransformer or its' load to short out.

RE: Three phase autotransformer

Suggestion: Please, would you elaborate on transformer connections, e.g. Autotransformer connection, center tapped delta power source connection, (open delta versus closed delta)?

RE: Three phase autotransformer

(OP)
Hello jbartos,

My sources can be three phase 60 Hz.Y or delta at 208V, 240V, 480V, & 575V(Canada). I assume that I won't be able to use corner grounded 240V delta.

My load will be a three phase Y connected refrigeration compressor operating at 440 V 60 Hz. (European design)

The autotransformer has all of the above taps for the input voltages and for the 440 V output. It also has a non-grounded neutral.

I plan to tap one of the 440 V phases to develope, via another single phase autotransformer, 230 V for control boards and ventilating fans.

RE: Three phase autotransformer


Suggest obtaining a commercial 480∆-240∆ dry-type transformer reverse fed with taps adjusted for lower ratio.  
  

RE: Three phase autotransformer

(OP)
To: busbar
From: pragmatist

It looks like you are recommending an isolated transformer to get around the different kinds of three phase systems; grounded and ungrounded, that might be found in the US. Is this correct?

RE: Three phase autotransformer

Suggestion: The dedicated transformer secondary load, e.g. a compressor, does not have to have grounded transformer secondary neutral.
The primary voltages are just a matter of correct taps.
The range of transformer primary voltages is suitable for an autotransformer. It will be smaller than a regular two winding transformer. There is a chance to save some money on shipping.

RE: Three phase autotransformer

While the compressor motor's power circuit doesn't have to be grounded, the control circuit does per the NEC.  Therefore, if the power source is ungrounded a control-circuit transformer will be required.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources