Water Mist application for large area
Water Mist application for large area
(OP)
Dear friends,
my problem is to protect some cable cellar with a Deluge Water Mist System.
The largest area to be covered by a system is 26m x 66m x 4m h whitout any fire partition (at this stage).
I would like receive some recommended solution for fire detection and extinguishing application to solve this matter.
Moreover in the plant is available an internal Firewater system operating @175 psi and an internal compressed air system.
Thank you.
my problem is to protect some cable cellar with a Deluge Water Mist System.
The largest area to be covered by a system is 26m x 66m x 4m h whitout any fire partition (at this stage).
I would like receive some recommended solution for fire detection and extinguishing application to solve this matter.
Moreover in the plant is available an internal Firewater system operating @175 psi and an internal compressed air system.
Thank you.





RE: Water Mist application for large area
Intellegent Laser type very early warning or air sampling
Most developed Mist Systems for this app:
Fogtec
Hi-Fog
Sercuriplex
The first 2 are high pressure systems with their own pumps, Securiplex uses compressed gas to shear the water droplets. No one else in North America is currently ahead of these 3 systems as far as testing. All produce a very fine mist.
Mist does not conduct any significant amount of electricity, Fogtec have test sheets for it. Of course once it accumulates it could. Fogtec have also done a pile of cable testing with/for ? VDS in Germany. The other companies may have as well but I don't know their story as well.
Ken