Any comments as to what the allowable deflection should be for a steel frame, fixed at base that will support high tension electric lines?
Kind Regards,
Lutfi
Kind Regards,
Lutfi
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: allowable defelection
I would check two items:
1) That the distance from the deflected power lines (at maximum sag) to any not insulated object complies with the clearances specified on the Electrical Code.
2) That the frame is stiff enough not to produce a dynamic problem if the presence of wind or seismic loads.
The deflection of the frame is going to be small when compared with the change in sag and lateral sway of the lines.