40 ft of peat at tip of landfill
The 40 ft deep of peat is between the toe of a landfill and a small creek. The landfill slope is about 200 feet long and parallel to the creek. The distance between the tip and creek bank is about 30 to 50 feet. The outslope of the landfill is 4H:1V.
10 ft deep x10 wide hardfill (concrete debris) with clay trench behind the hardfill was placed between the landfill and creek to cutoff any leachate path (based on preliminary knowledge that the peat was only 2 to 10 feet deep). After the installation of the hardfill trench, it is observed that the hardfill sunk about 3 feet and the creek bottom heaved up. The creek has to be excavated to maintain flow.
Now we need to build the contamination trench about 40 ft deep with hardfill in front or behind to cutoff any leachate flow and to save the creek runing. How to build the trench and berm in such depth and scope in a landfill site. I am considering two issues, one is constructibility, the other is safety of construction. Also, geotech issues such as displacement or in-situ operation methods other than removal and excvavation earthwork.
Any suggestions or thoughts or inputs will be very appreciated.
CSZ
CSZ
RE: 40 ft of peat at tip of landfill
A steel sheet pile wall looks to me to be the best overall solution; there are lots of things I don't like about this approach, but it seems to solve a lot of your problems while addressing the environmental and site safety issues. Removal and replacement of the 40 feet of material is a non-starter - too risky. The same goes for a concrete diaphragm wall.
A sheet pile wall has one big advantage - that can also be a liability. It's flexible.
What options have you considered?
Focht3:
Thanks for your quick response of this posting. We do consider sheet pile wall as one of the options. However, our other concerns over the options also include the stability issues of the landfill. Current phase construction is increasing the height and push the toe of the landfill a litle further towards the creek direction. The multiples issues related to slope stability, settlement and movement of the peat materials, uplift of the creek bottom, leachate containment and collection, constructibility and cost, etc, lead us to examine any other engineering solutions.
Lateral stability can be increased by installing some sheet pile sections perpendicular to the main 200 foot long alignment; they will act something like anchors or braces (depending on which side of the wall they are installed.) Or you can install one or more walers and large H-piles to increase the lateral stiffness.
There is no cheap fix for this one -
Another "wierd" way is to make a structural channel for the stream bed in the 200 ft. whereby the stream bed elevation is supported on the underlying material. Use wood piles (always under water so won't rot), then a concrete slab atop with sidewalls. Do architectural stuff to make it look like a stream again. Sounds expensive but may not be - wood piles are not too expensive, normally. But, expensive - so is sheetpiles and it is only 200ft long - not that big. They do this kind of work for large rainwater sewer outflows in built-up areas (Rambo Hagar in Hamilton Ontario).
BiG H: The Japenese product is fujibeton. I had discussions with representatives over twelve years ago. At the time we were do do a trial section in muskeg but it did not materialize.
Just a thought. Is it possible to place a culvert (csp)(steel) in the channel and berm over. This would have the effect of reducing the likelihood of upheval of the creek and would allow the creek flow to be maintained. Berm will also cause consolidation of peat.
Having said all that, the owner may elect to try one of these cheaper approaches. After all, they are probably more concerned with cost than "fix it once and for all."
csz: If the owner elects to use one of the "cheap" methods instead of a steel sheet pile wall, be sure that you thoroughly document all the potential problems that could arise. You will need to cover your backside.
You might find a bentonite:cement:soil slurry wall is
cheaper than sheet pile, more flexible and leak-tight.
Figure about $200 a running foot, and no call backs.
As the landfill pushes closer, might use a geotextile-
wrapped native borrow berm on the slurry wall (trench),
you might have to excavate down the creek thalweg if it
heaves up after the berm is placed. Without a drainage
gallery in the advancing landfill, leachate will just
build up until it overtops the berm, so pencil that in.
No rigid structures will work in those soil conditions.
USER ASSUMES ALL LIABILITY FOR USE OF THESE OBSERVATIONS.
VAD - thanks for help on the name; I was in the right ball park for a 17 year "lapse".
Yes, a "movement independent" design could be developed - but as you point out, the issue is cost. And risk of failure is a concern to me. I look forward to hearing how csz solves the problem -