UPS Systems
UPS Systems
UPS Systems
Can anyone link a basic design guide for UPS systems?
It would be much appreciated.
Thanks.
RE: UPS Systems
How is this connected?
My building voltage is 277/480,3ph,4w and they need a panel which is UPS protected.  So I can connect this like a transformer?
I'm not sure how to show this on a one-line.  Just like a transformer?
I assume it would be like a generator with a transfer switch which would switch over to the UPS?
RE: UPS Systems
I saw that diagram.
Does the UPS have the isolation transformer integral to it?  Does it also have the circuit breakers integral?
I only need one panel (computer loads) connected to a UPS.  So, would I connect thru the UPS or have a transfer switch.  I am assuming directly thru it.
RE: UPS Systems
[Does the UPS have the isolation transformer integral to it?]
Yes
[Does it also have the circuit breakers integral?]
Yes, everything shown on the diagram is included, you only need to bring in the utility power source and the cables to the load.
[I only need one panel (computer loads) connected to a UPS.  So, would I connect thru the UPS or have a transfer switch.  I am assuming directly thru it.]
Then bring the cable from the panel originally destined to the computer loads to the UPS instead, and the output of the UPS to the loads.
RE: UPS Systems
Try IEEE Std 446, Recommended Practice for Emergency and Standby Power Systems for Industrial and Commercial Applications.
RE: UPS Systems
Thanks to everyone.