VAV and Dual-Duct system calculations

VAV and Dual-Duct system calculations

VAV and Dual-Duct system calculations

(OP)
Could anyone give me some clues and rule of tumbs for VAV and Dual-duct hvac system design? Can you please specify where can I find comprehensive calculation details of how sizing cold and hot air ducts and selecting appropriate units for commercial and school applicatios using these type of systems?

thanks

RE: VAV and Dual-Duct system calculations

mitcham,
Do you have access to a set of ASHRAE manuals?   If not, try starting here:
                http://www.ashrae.org/

RE: VAV and Dual-Duct system calculations

Why do you want to go dual duct? This waste energy because of simultaneous heating & cooling. Also the system uses more space & more ductwork. Go VAV instead. You may need reheat (for heating loads & to avoid dumping at diffusers) but this would be at the VAV box minimum volume.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources