3 Ph.Transformer Backfeed

3 Ph.Transformer Backfeed

3 Ph.Transformer Backfeed

(OP)
I'm looking for reference material on 3 phase transformer backfeed.  For instants, I had a three phase bank 120/240 (gnd Y/closed delta...75/37.5/37.5 kVA) and lost one phase on the high side of the bank.  Oddly enough, the phase that the cutout had isolated was actually at a higher voltage then other two phases.  It's a classic delta backfeed situation.  However, I'd like to show how this happens on paper (phasors, etc.)...for this and other TFR connections.
Thanks in advance....

RE: 3 Ph.Transformer Backfeed


See §4 of ANSI/IEEE C62.92.4-1991 …Application of Neutral Grounding in Electrical Utility Systems, Part IV—Distribution

For the described reason, it is listed in IEEE C57.105-1978  …Application of Transformer Connections… as a “problem connection” for it acts as a very good zero-sequence source on the wye side.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources