mag flow meter justifications

mag flow meter justifications

mag flow meter justifications

(OP)
Hi,

Our approving authority doesn't put flow meters in their district water pump stations, and there are no residential meters either -- we all just pay a flat rate for water. I recommended a magnetic flow meter on the discharge mainfold for a pump station design because I want it for start-up, future troubleshooting and monitoring, etc.

Other reasons I have to justify it are:
1) Pumps operate at different points over time
2) The design and assumed suction & delivery pressures, voltage may have little or no relationship to such estimates during future operating conditions.
3) A flowmeter can enables assessment of potential savings in energy costs.

Are there other reasons than you can think of?

Thanks

RE: mag flow meter justifications

drain:

what is the magnitude of the problem?  what kinda flows are at the stations?  No putting flow meters on large assets like a pump stating as a rule is kinda funny...I was just curious to see how bog the stations are to see just how funny it is...lol

You hit the most important reasons.  not knowing what the pump is doing is a definate safety problem since you have really no true idea what is going on.  you could be coiling the water at shutoff head and no flow and boom...now that is an extreme...but worse has happened when the maintenance and operation people are disconnected from the equipment in such a way as that in not having the right equipment to do their job......

BobPE

RE: mag flow meter justifications

(OP)
Initially we have 650 usgpm (one duty pump), but we've got pads for two more duty pumps. High head - about 430 ft.

Do you know what the main differences in quality might be between a $3,500 and a $1,500 meter? It's not apparent to me.



RE: mag flow meter justifications

1. Accuracy of the meter.
2. Turn down ratio.
3. MOC and internal lining.
4. How many electrodes inside. (for partial flow detection)
5. Electronics
6. Brand Name

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources