DTIs that were installed incorrectly
2

DTIs that were installed incorrectly

DTIs that were installed incorrectly

(OP)
I am being consulted on some DTI (Direct Tension Indicators) that were installed as follows:

1.  ¾ inch diameter A325, for slip critical joints, contractor used DTI
2. Contractor installed DTI under nut which is not the best application
3. Contractor did not use a hardened washer between DTI and nut (turning element)
4. Contractor asked DTI manufacturer to duplicate the filed condition using Skidmore tool
5. Test results from six (6) bolts indicated that only at tension of 34 kips; the feeler gage had refusals to qualify proper tension

Does any one have words of wisdom? There are many bolts that already installed. Your quick response would be greatly appreciated.

Good night

RE: DTIs that were installed incorrectly

2
Lutfi...I would look at two parameters.  One, do the test again with Skidmore-Wilhelm device but put DTI under bolt head to see if different value obtained.  Next I would inspect the 6 tested assemblies to see if any smearing or galling on the DTI from the nut rotation.

Look at the torque values to see if they are reasonable. If somewhere around 400 ft-lb (+/- 25 ft-lb) then in reasonable range.  If way above that to achieve tension, maybe the DTI's are faulty.  Then you can check hardness of DTI's to evaluate.

RE: DTIs that were installed incorrectly

(OP)
Ron,

Thanks for th input. I like the idea of testing the DTIs under the bold head. However, I am not sure if I can use the "torque" word anymore since everybody is using "tension" including AISC and RCSC. I used the torque for many years, actually over 23 years without any problems.

Thanks again.


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources