1.What is the effect of a lightning
1.What is the effect of a lightning stroke on the system voltage in an EHV network.
2.What do the following terms refer to in a power system:
i. strong source
ii. weak source
i. strong source
ii. weak source
RE: 1.What is the effect of a lightning
2. A strong source is a source with a very small impedance. A weak source has a large source impedance.
-The speed of propagation of the transient wave is a function of the distributed constants of the conductor. That is the Velocity = 1/(LC)^.5 where L is in henrys and C is in Farads. The velocity in an open conductor is approximately 1,000 Ft. per microsecond( which is at the speed of light) and in a cable it is approximately 500 Ft. per microsecond-still fast but only half the spped of light. Ref. Lightning Protection for Electrical Systems, Edward Beck, pg.297.
-The lightning wave does not necessarily destroy everything in it's path. The arresters installed on the system usually safely conduct the transient safely to ground.
-The ability of an arrester to transfer a charge to ground is determined by a combination of the arrester resistance, the current discharge capability of the arrester and the maximum temperature rise that the specific arrester can withstand. Having said that, there is no standard method for measuring the joule rating of their arresters-each manufacturer appears to have a different method. The standard for surge protective devices does not specify a standard. I understand that several working groups are attempting to quantify this problem.
-Dr. Lubo Kojovic of the Thomas Edison Technical Center has recently presented a paper at the IEEE Winter Power Meeting (Feb.2001)and is suggesting that and I^2t rating may the answer. I personally like that approach.
Some interesting data on lightning:
-There is a worldwide average of 44,000 lightning storms per day.
-There is a worldwide average of 100 lightning strokes per second.
-The U.S. average is reported to be 29.5 million strokes per year which is roughly one stroke per second. The majority of these strokes occur during the months of May-Aug.
-Lightning is the principal cause of fires in rural areas.
-Average chance of being killed is 1 in 350,000.
1. Fink D.G, Beaty H.W. "Standard Handbook for Electrical Engineers," 14th Edition, McGraw-Hill, 2000, Section 27 "Lightning and Overvoltage Protection"
The lightning is considered an external surge, Reference 1, apart from internal surge due to switching. All surges must be considered. The lightning stroke can be mitigated or avoided by the following:
Mitigated by:
1. Air (Spark) Gap
2. Gapped Surge Arresters
3. Metal Oxide Varistor (MOV) Arresters
Avoided by:
1. Lightning Rods
2. Proper grounding and shielding
Temporary lightning overvoltages may have an envelope to about 3.3 p.u. of voltage rise, and duration of about 10**-4 second. Temporary switching overvoltages have an envelope 2.6 p.u. of voltage and up to 10**-2 second. Reference 1 deals with this topic on 77 pages and provides Bibliography and References.
Strong source has a relatively small internal impedance and a relatively high short circuit MVA.
Weak source has a relatively high internal impedance and a relatively low short circuit MVA.
Magnitude of Direct Strokes Recorded on Transmission Lines.
Here is some additional information concerning ligntning strokes to transmission lines within the U.S.
1% of the strokes = or> than 111,000 amperes
5% of the strokes= or > than 63,000 amperes
10% of strokes = or > than 50,000 amperes
20% of strokes = or> than 33,000 amperes
50% of strokes = or > than 14,000 amperes
70% of strokes = or> than 9,000 amperes
The maximum recorded stroke to a transmission line was 218,000 amperes.
The maximum recorded stroke to a structure was 345,000 amperes and it was recorded at the Cathedral of Learning at the University of Pittsburgh where Westinghouse had set up an observation and measuring lab.
Wave Fronts of Direct Strokes
8% of wave fronts = or > than 6 microseconds
23% of wave fronts = or > than 4 microseconds
62% of wave fronts = or > than 2 microseconds
90% of wave fronts = or > than 1 microseconds
Wave fronts less than one half microsecond and more than 10 microseconds have been recorded.
Polarity of Strokes
Approximately 90 % of all lightning strokes have negative polarity and the maximum strokes recorded were of negative polarity. In general positive strokes are of low current magnitude
Stroke Mechanism
The typical lightning stroke si composed of three portions. The pilot leader, the stepped leader and the return streamer. The propagation velocities of these three portions are:
-pilot leader averages app. .5 ft. per microsecond
-stepped leader averages app. 30 ft. per microsecond
-return streamer averages app. 100 ft. per microsecond
And the average length of the stroke channel si 5,500 ft.
One very interesting fact about lightning as studied by Dr Mousa of BC Hydro is that if the shape of the structure is conical the return stroke is not developed. Thus the less effect on such structure. Coincidentally, in most of the East and South Asia, there are idols of Buddha, where an idol of thunderbolt is kept. The mythology is: Buddha captured one of the thunderbolts and there is no possibility of lightning in such area. Even if they are located in lightning prone areas, I do not know any lightning had hit such area, but the structures are very conical!
One more interesting fact is that in some high voltage lines below 38 kV many utilities are using ground conductor at the top of the structure in order to shield the lightning. In fact the ground conductor even if it shields, is of no use as the voltage raised by lightning to the conductor is enough to have back flashover to the line conductor.
So the only way to deal with lightning is to accept it as it is and have very good ground.