Conductor Withstand Ratings

Conductor Withstand Ratings

Conductor Withstand Ratings

(OP)
I have a situation where the conductors that I am trying to qualify have the possiblity of seeing locked rotor current for a maximum of 100 seconds. Does anyone know where to find short term withstand ratings for copper conductors?

RE: Conductor Withstand Ratings

The Okonite Company have an "Engineering Data For Copper and Aluminum Conductor Electrical Cables" Bulletin 721.1 With Section 4 discussed and plots the allowable Short Circuit Currents for insulated copper conductors + the equation. It is probably now located on there web site.

RE: Conductor Withstand Ratings

Also look into any edition of "Standard Handbook for Electrical Engineers".

One point often overlooked when determining long-time temperature exposure effects on cable, is that the connectors are more likely to be overstressed, than are the cables.

Another point of concern is the the increase in length of long cables.


RE: Conductor Withstand Ratings

I noticed from the IEEE STd 141, the same formula is used as was shown in the Olkonite Sheet, However the IEEE has the caviot that this formula is only good to appproximately 10 sec. Sorry

RE: Conductor Withstand Ratings

The formula is only good for short time periods because it assumes no heat loss from the conductor.  It would be conservative (maybe too much so for 100 sec) for longer time periods because there will be heat loss.

RE: Conductor Withstand Ratings

JosephKendall,

An excellent treatise on the subject was presented in the April '79 issue of EC&M (Electrical Construction & Maintenance) magazine.  It was presented by Dr. K.D. Srivastava of University of Waterloo, in Canada.

Four graphs show that a straight-line relationship between time and current, plotted on a log-log scale, also can be found for short-time overload... defined as being from 10 to 1,000 seconds.

Thus, if you have access to the typical Short-Circuit stress curves, then, by extending the time axis, you can determine the over-load thermal capability line for the cable & current condition you are concerned about.

RE: Conductor Withstand Ratings

BTW, the four graphs represented conductor materials of copper & aluminum, and typical NEC-code listed PVC insulations such as TW or THW, and XLPE insulation such as XHHW.

A rather complex temp-rise formula is also presented.

RE: Conductor Withstand Ratings

You may find the article at the end of this link  (http://www.usawire-cable.com/techpapers/tempratings.htm) of interest. It deals with three different time frames: Normal; emergency overload; and fault conditions.

Since the emergency overload is "long duration", this may be what you seek.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources