Please confirm if the following statements are true.
I would like to operate a 380Vac 3ph 50Hz 1500rpm motor on a 440Vac 3ph 60Hz supply. I believe that this motor wil run on the 60Hz system at a lower current (20%?) and at higher speed 1800rpm (neglecting slip).
The control power transformer and CTs will need to be changed out as per the voltage changes as well as the overloads (will see less current).
There may be an issue with starting torque; the 50Hz (on the 60Hz supply) motor may not deliver the equivalent torque that a 60Hz motor of the same horsepower would deliver. True/False?
Your input would be greatly appreciated.
Lance,
I would like to operate a 380Vac 3ph 50Hz 1500rpm motor on a 440Vac 3ph 60Hz supply. I believe that this motor wil run on the 60Hz system at a lower current (20%?) and at higher speed 1800rpm (neglecting slip).
The control power transformer and CTs will need to be changed out as per the voltage changes as well as the overloads (will see less current).
There may be an issue with starting torque; the 50Hz (on the 60Hz supply) motor may not deliver the equivalent torque that a 60Hz motor of the same horsepower would deliver. True/False?
Your input would be greatly appreciated.
Lance,





RE: 50Hz motor running on 60Hz system
Please consider a keyword search at this site. It has been extensively discussed here.
RE: 50Hz motor running on 60Hz system
Thread238-49838
and follow thru on others, therein
RE: 50Hz motor running on 60Hz system