Methane extraction system
Methane extraction system
(OP)
Does anyone have any tips or references for design of a methane collection system below the ground floor of a building (built on organic fill). I know we have install perforated pipes to mechanically vent the sub-floor, but that's about it. Thanks in advance.






RE: Methane extraction system
This document has some information in that should help. One of the systems I saw included an exhaust fan that ran continuously to keep the CH4 concentarction below the Low Flammability value. This was installed after the plumber started a fire and explosion when he lite a cigarette, droping the match into the sump.
Methane came from construction waste buied in a trench in the back yard and a warm moist spring (High water table)