Hello,
I'm searching for a schematic which let me drive a +24Vdc relay with only +12Vdc. The relay characteristics are the followings:
Unom = 24Vdc
Upull-in= 16.8Vdc
Uhold = 8.4Vdc
Urelease = 2.4Vdc
Inom = 16.7mA
Coil resistance = 1440 Ohms +/-10%
UMAX Coil = 60Vdc

Thank You already for the feedback

RE: Relay driving

If you don't have 24 Vdc, why are you using a 24 Vdc relay?  

According to your spec, you need a minimum of 17 V to engage the relay.  You'll need to either get 24 V or generate 24 Vdc using a separate switching regulator.

TTFN

RE: Relay driving

(OP)
I'm using a 24Vdc relay because the consumtion is lower than a 12Vdc one !!!
A switching regulator is useless there is a very simple and better solution and I found it. Thank You for your help at all. Bye

RE: Relay driving

(OP)
The solution is the following a transistor which put a capacitor (already filled with the power supply voltage) in serie with the power supply you have. So, you'll get the dubble of the voltage. The relay will go in the 'ON' state and at the "same" time the capaitor will be filled again.

RE: Relay driving

The voltage doubler will only work if you can store enough energy in the capacitor to pull in the relay.  

For the same relay, a 12V coil and a 24V coil will require the same amount of **energy** for pull-in and holding, regardless of the operating voltage.  

Also, be aware that the relay coil will deliver a powerful voltage spike to your circuit whenever you de-energize it.

RE: Relay driving

Is there a latching version of the relay? If so, you only need to pulse the coil long enough to actuate the relay then no power is drawn at all. Such relays are usually magnetic latching. Single coil versions set their state depending on polarity while two coil versions require simpler drivers. The capacitor charge pump scheme should work fine as long as the capacitor has time to charge before cycles and does not disintegrate later due to high surges. It will still have many times the power consumption of a latching relay solution.

RE: Relay driving

2
' a transistor which put a capacitor (already filled with the power supply voltage) in serie with the power supply you have. So, you'll get the dubble of the voltage.'

Duh, I think you'll get some extra current available to pull in that 12v relay, but I doubt you'll see any voltage dubbling to operate a 24v coil.

Now you could jump your unregulated voltage over your regulator to drive the coil, but your power requirements are going to be similar regardless of your coil voltage.  

RE: Relay driving

(OP)
All right. I will try to answer all at one time.
That's true and I have calculate the capacitor value (220uF). In fact a relay has to be driven with current, the voltage is not so important. So, after be pulled-in the relay consumption will be 5.85mA for a 24Vdc and...11.69mA for a 12Vdc! My problem is that the power supply can only give 21Vdc to 31.5Vdc (30Vdc typical) with a MAX current of 250mA (minus 50mA for the rest of the circuit = 200mA for the relayS (yes, there are 4 relays which must be driven)) I can't jump to the unregulated voltage (no acces, I just receive cables which deliver what I wrote upwards)
The problemS with a latching version are that it is MORE expensive than a "normal" one + that the relays must be OFF if the main power falls down and I don't have enough energy in this case to switch all the latching relays OFF + also I know there is a circuit doing this but then the devlopment become too expensive; it has to stay low cost.
Oh yes one more thing, a 24Vdc relay with a 1296 ohms coil (=1440 -10%) has a hold current of 5.85 mA thus a power of 49.14 mW a 12Vdc one has a power of 98.28 mW in the same situation (HOLD). At last but not least, I didn't forget to put a free wheel diode.
Best Regards to all of you.

Yves

RE: Relay driving

Now lets see, 24v x 5.85ma = 140, and 12v x 11.69ma = 140, kind of looks like similarl power requirements.

At 12 volts, your 4 relays are going to require 11.69 x 4 = 47ma. You say you have 200ma available.

Voltage is a equally important in relay coils as it produces the motion of your contacts. Current then holds the contacts in place.

Tell us again, why do you want to go with a 24v relay in a 12v circuit.

RE: Relay driving

(OP)
Yes, indeed you're right.But the 12Vdc relay has a max voltage of 30.6Vdc while the 24Vdc has a max voltage of 61.2Vdc. Because the voltage I receive is 30Vdc +5% -30% I prefered to choose the 24Vdc one. 30Vdc minus 30% is 21Vdc and that's also above the 12Vdc nominal of the 12Vdc relay, but just under the nominal voltage of the 24Vdc relay and enough above the 16.8Vdc that its requires to pull-in. So I find that the 24Vdc is the best one in this case.

RE: Relay driving

I don't know about the rest of you guys. But I am totally lost as to what tensi is talking about. Are you saying you have a fluctuating voltage ? What kind of system is this ? What is the application ? Perhaps a relay is not the answer for your circuit. Is this perhaps an undervoltage relay ?

RE: Relay driving

Seems like a voltage regulator (cheap) or even cheaper a series resistor with the power supply would be the way to go to reduce the voltage down to something useable for the 12VDC coil or even a zener.
I think your creating way to much work to use the 24VDC coil. Besides putting a cap in series with a 12VDC supply will not give you 24VDC, the cap simply charges up to 12VDC then current flow stops. The cap + is then tied directly to the power supply + (remember Kirchoffs law). If you put the cap in parallel with the supply it will give you a little more current capacity at relay pull-in but thats it.
Go with something to reduce the available DC supply to something reasonable for a 12VDC coil.

RE: Relay driving

I think that he is saying that his incoming power supply allows him to use a 24VDC coil without any type of conditioning.  If that is the case, then 24VDC is the way to go.

To control it, use a transistor to activate the coil.  The 12VDC logic signal can be voltage divided down to work with the transistor you choose.  Let me suggest using a power device...

RE: Relay driving

the original question was '...drive a +24Vdc relay with only +12Vdc.' Some good suggestion where put forward, but for some reason the criterim keeps changing. The problem we have here is not with the circuit my friends. I've learnt years ago, that to effectively troubleshoot a condition, you need to understand the basics.

RE: Relay driving

(OP)
I'm sorry guys but I'm still looking for a schematic which let me drive a 24Vdc relay with only 12Vdc.
OK! By writing this I just understand my error! I'm really sorry for this ! Because englsh is not my mother language I was focusing on what I was writing in place of the data I have to give. Sorry again !
So, you must imagine a box with inside a controller, 4 leds, 4 push-buttons, resistors, capacitors (1 of 330uF/35Vdc for the relays) 4 relays, 2 connectors.
The power supply is the one I describe upwards and I can't do anything to it. Now, the worse (that I forgot to tell) There are 10 boxes this means 40 relays which have to be activated! The lower voltage I receive (and is guaranted) is 21Vdc (30Vdc -30%) the maximum is 31.5Vdc (30Vdc +5%) the current is 250mA and I reserve 50mA for the 10 controllers and the 40 leds. I have NO place to put al lot of components on the PCB (because the clearance between the very low power and the main that the relays have to switch) the PCB is about 75mm x 30mm and I have to use it dubble sided to design the traces because the relays have to switch 230Vac (+/-10%) 16Amps!
I know there is a schematic with only 1 transistor and its base resistor, a capacitor, ??? (the rst I don't remember) and this small circuit put the resistor (which is filled with the voltage of the power supply) in serie with the violtage of the power supply just to pull-in the relay. after that the relay stays ON because is hold voltage is lower than the voltage of the power supply which rests.
I hope this is more clear for you now. One more time sorry and be sure this is not a joke and I'm really into the shit now because time flows and I still have nothing to show to my project leader. Once I will remember the schematic I will give it to you also. I don't like to waiste my time and so I don't want to waist the time of others also. Regards to everybody. Yves

RE: Relay driving

Your request is still not clear. You say you have 30VDC available but you want to drive a 24VDC coil with 12VDC. Makes no sense. I purpose the following based on what you have.

So, you have 24VDC available but are using 12VDC because of the so called lower current draw? The current draw of most relays goes down as you increase the coil voltage. If you look at a basic relay, http://www.midtex.com/pdf/midtex/pcb/pdf/496.pdf
the current draw of a 24 volt coil is exactly half of that of the 12V coils.

If you want to use 12V coils still, then use a regulator, zener, or series resistor to reduce the voltage to the 12VDC relay coil.

If you really need to drive a 24VDC coil with only 12VDC then you have some work to do. I have not heard of a simple circuit to drive a relay coil based on one transistor. Maybe your thinking of using the transistor as an amplifier or something. Still will not work.
Good luck.

RE: Relay driving

- Are you using 12VDC or 24VDC relays?

- How much current can your supply source?

- What are you using to turn on your relay (voltage level, current source / sink ability / frequency / etc.)?

- Why does it have to fit in this box that you describe?

RE: Relay driving

I hear what your saying about wanting to use the 24v relays to meet your current ratings. But here's the deal, calculate what your maximum power requirements are, ie: the max number of relays on at any one time. If possibly all 40, @24v coil / 5.85ma, plus your 50ma control/led, that requires approx. 5.7 watts.

Your power supply is capable from between 5.2 (21v x 250ma) and 7.8 (31.5v x 250ma) watts. At the 5.7watt end of things, you'll be browning out, and possibly sooner. If any safety issues are about you can double that.

If your indicating (it's not clear) that your power supply is falling from 30v to 21volts as you draw from it, then your supply is simply underpowered. Your only option then is to insert a capacitor large enough to average the duty cylce of your load, on your supply line. If your average power exceeds your supply, pull out your purchase aquisition form.

RE: Relay driving

(OP)
I never guess that it would be so difficult to make me comprehensible! I thought that what I was writing was clear. My first question was, in fact, a schematic which let me drive a relay (whatever which one) with the half of the voltage it need. I didn't give more infos because I thought it was not necessary. But... when I look at aal the responses !!! I was wrong and still be !!!
One more precsion now for "automatic2" The 50mA I have reserve are for the 10 boxes (10 microcontrollers, 40 leds)
The characteristics of the power supply I "receive" are what they are I can't do anything to that. So are the specifications. What I wrote is that the power supply is a 30Vdc -30% +5% (that are the min & MAX values it can reach)
So, I take the worst case for my calculation. The same with the relay. By the way I found one which has a coil of 2300 Ohms +/- 10% (2070 < 2300 < 2530) In this case also I take the lowest value because it is when the coil value is 2070 and the voltage 31.5 that it would take the most current. For me the worst caseS are first when I have only 21Vdc 200mA (50mA reserved so I don't count them) with which I have to pull-in and then hold 40 relays with a 2070 Ohms coil (at the same time (worst case also)) and at the other side 31.5Vdc 200mA and the same story.
From there my idea of a schematic which let me drive a relay with the half of its nominal value. I finaly found it. But I don't know how to put a schematic here. It is the first time I use such forum. My idea is even to use a 48Vdc relay so the pull-in is 33.6V and the hold 16.8V and the current is half of the current of a 24V relay.

RE: Relay driving

So what do you have to drive this?  No, you havent provided much useul imformation!  I've done a lot of these relay tricks to reduce power consumption but you usually pay wit a number of extra parts.  If you have a microprocessor, you can turn the driver on full initially and then pulse it, PWM mode, to reduce the current.  You can also have a parallel cap and resistor in series with power to the relay.  Of course these work only with a relay that is the same as the supply voltage.  Charging up a cap and then putting it in series is an easy trick if you are just using a switch.  It is a lot more parts if you do it with electronics. I think the purpose of engineering is to do the design before you order the parts.

RE: Relay driving

can you state:
min and max supply voltages and curents
what relay you intend to use and the specs for that relay
can you get a different supply? as aposed to changing an existing one.

RE: Relay driving

(OP)
I have to re-use existing used relays. I'm not sure that PWM will help to reduce the consumption. I've read that the hold current must be at all times above the minimum holding current.So, each time it would be under that value the MAX peak should be higher. This means that I win nothing. The charging cap solution is not applicable because of the lak of place.

RE: Relay driving

You say you've found your circuit. Even though you may not be able to post it, please explain so we can see how you've created power where there is none.

RE: Relay driving

I would be very interested as well!  Unless you have some sort of booster, or a postive and negative supply, those relays need the voltage to work.

RE: Relay driving

For using PWM, the switching time must be less than the release time, then it will work fine as long as the average (DC) current is above the minimum hold current/voltage.

Something worth mentioning, if your planning on energizing all of these relays at the same time with power source you have, I do not believe it will work. At least with solenoid type coils, they can pull up to 20 times the nominal current at energizing. Your power supply will not like energizing all of these at the same time.

If you do not need all to come on at the same time, of if you do, you might try some large capacitance in parallel with the source. The cap will charge up to power supply voltage. When the switch between the coil and supply is closed, the cap will supply some extra power to pull-in the relay. Presumably, the power supply votlage will fall off when relay is introduced in the circuit but the cap will already be charged to the highest voltage available. Note: you may have to put some small resistance in series with the cap to limit the current when the power is applied across the cap (depends on cap size and mfg).


RE: Relay driving

(OP)
have a look at http://www.piclist.com/techref/io/relays.htm
and but there is a fault in the schematic (the cap near the relay must be take off and there must be a free wheel diode on the relay coil also the diode near the undesirable cap must be also be taling off)and the left side of the resistor must be connected to +12 and at the other side of the resistor must come the collector of a transistor; its emittor to the ground , and a resistor at its base. So the circuit can be driven with +5Vdc. I hope this is clear... sorry if not. But I even doesn't need it.

I don't agree with automatic2. There is power and energy but not enough. Just remember that I have 200mA MAX.The trick is not to switch the relay at the same time. One relay per box, thus 10 relays at time. Each relay need 16.8V to pull-in (I have mimnimum 21V) and 8.12mA (the minimal coil value is 2070 ohms) thus 81.2mA for 10 relays (during 20ms). After that hold voltage: 8.4V and 4.06mA (the coil value didn't change) thus for 10 relays 40.6mA. Now the next 10. Thus, 40.6mA + 81.2mA = 121.8mA (during 20ms) after that 81.2mA. The next 10. Thus, 81.2mA + 81.2mA = 162.4 mA (during 20ms).After that 121.8mA. Now the 10 last. 121.8mA + 81.2mA = 203mA (during 20ms) here overflow of 3mA during 20ms ! (I resolve this with a capacitor of 330uF) After this time 162.4 mA. And now I have 40 relays in the ON state ! What do you think about it?

RE: Relay driving

(OP)
The relay type I use is a ZETTLER AZ 764-1AE-24DSF

RE: Relay driving

Your little trick may be feasible, but is vastly different than where you began. If your referring the the 'junk box' circuit, I'd like to know how you get the -5 volts (-12 in your case).

RE: Relay driving

He is absolutely right!  The 47u is fully charged to 5V.  Once the transistor turns on (which must be fast), one side of the cap gets forced to ground.  Since the cap will resist instantaneous voltage change, it will cause the other side of the cap to be 5V lower, i.e. -5V (since the 100 ohm resistor prevents a direct connection to ground on the inductor / coil side).  For a short time, the voltage across the coil will be creater than 5V.  The only things that I see that prevent this from being a straighforward solution is:

1)  The 5V control / supply signal for the coil must be able to be quickly turned on / off & supply enough current to not be "browned out".

2)  The turn on time of the relay must be fairly small, like 100 micro seconds.  Increasing the cap could increase the negative supply.

3)  The turn on voltage must be as low as 8V.  This circuit will not produce exactly -5V, but closer to -4V on the bottom of the coil.  Therefore, to have some margin, the coil should energize down to around 8V.

Otherwise, this is a wonderful circuit and I will keep this one in my personal library!  Tensi, you get a star for sticking to your guns and backing up what you claimed!!!

Excellent thread!

BTW, I was able to verify the theory by running a simple simulation with PSpice...

RE: Relay driving

(OP)
Hello everybody! Thanks a lot for the star I receive!
I've tried another solution but have to test it deeper before; just to be sure...
Using PWM can spare a lot of energy. A relay may so be driven at a frequency which may not be under the 100Hz. I made a try at 10KHz with a duty cycle of 50/50. So the current used by the relay is half of what it need!
I made already some measurements and what I measure is near what I calculate. But like I said upwards(?I'm not sure of these word) I have to try it. See You after that.

RE: Relay driving

(OP)
Hello! I've made a lot of tests! You know already the context... The schematic is the following (where can I ask if it is possible to put a schematic or ask to devlop something that make it possible?) The power supply (+) line go to one point of the relay coil, the other side of the relay coil go (with a diode 1N4148 parallel on the coil with its cathode connected to the (+)) to the collector of a BC549 the emittor connected to the ground. The base with its resistor (1K) receive a square wave signal (f= 10Khz). There is a buffer capacitor 330µF/35Vdc between the + and the ground of the "power supply" . One capacitor for 4 relays. By variating of the duty cycle you can give the current that the realy need to work. When you measure you will see that the power supply just give a little more than the HALF of the current used by the relay. That's what I need ! By the way I choose a Zettler relay of 12Vdc i.p.o. 24Vdc because a 24Vdc relay need 22.3V to pull-in @+55°C and the lowest voltage I can get is 21Vdc. OK a 12Vdc relay need more current but with this system it is no more a problem ! ;-D
I hope this can help others. Don't be shame to write me @ yves_tensi@yahoo.fr if you need more infos/datasheets about relays. I think I will assemble all the infos and put them on a web page. I'm sure this will be helpful. Best regards to everybody who take time to answer my questions. I will be tracking this till the end of july. After that no more.

RE: Relay driving

So you've gone with a couple of the suggestions, PWM and the purchase req., great, don't be ashamed to think you might be humbled by speaking with some of us 'field workers'.

RE: Relay driving

(OP)
MIssunderstanding again! What I wanted to say is that you don't have to hesitate to ask me things. I give my e-mail because it is more easier to send files than to write a long explanation. I'm really soory if I hurt someone ; it was and is nver my goal.

RE: Relay driving

Do you notice any audible noise from the relay with a certain PWM frequency? I have seen circuits like this but never had the need for one. The ones I have seen, at some audible noise associated with them. I am sure there is some PWM freq where the noise is not heard. I would like to see a schematic of what you have come up with. You can email me at buzzybooper@excite.com. I would appreciate it.

RE: Relay driving

(OP)
buzzp, The schematic is very simple: Foom the positive point of the power supply dedicated to the relay(s) go directly to the coil of the relay the other side of the relay coil is connected to the collector of a transistor (BC547 e.g.) the emitter of the transistor is connected to the ground. Put on the base of the transistor a resistor calculated to give enough current for the relay. The other side of the resistor go to the µC. For experimentations you can replace the µC by a square wave generator. Don't forget to put a diode // on the coil with its cathode to the +. That's all. The frequency must of course not be too low. For my part I used a frequency of 1KHz. The trick is to play with the frequency. The way of measuring is also important. Just add a resistor between the + and the relay coil to measure the current which flows through the relay coil. Put a Ameter at the + of the power supply. You will see the difference ! I will try to scan the schematic and send it to you. Please be patient. Regards.

RE: Relay driving

Tensi,
 Okay it is all clear to me now. I now understand what you were trying to do. A schematic is not necessary. Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources