Condensate Receiver - mixing of makeup water
To all,
My questiona are about the mixing of "softened" makeup water in a condensate receiver tank. The boiler plant will have 70% condensate returned at temperatures from 15-185 degrees F
The receiver is an internally coated tank that collects condensate returned by a district heating system at an educational facilty.
Q1: Is the receiver the best location to mix the makeup water with the condensate and if so why ?
Q2: Is there any disadvantage to mixing of the condensate and softened water in the deaerator instead of the receiver ?
Thanks to all...
MJC
RE: Condensate Receiver - mixing of makeup water
The advantage of mixing condensate and make-up water before the DA is that you can smooth out spikes in the steam load that can occur with a big shot of cold make-up water hitting the DA. I've never really liked the arrangement. A well designed DA will have an arrangement for make-up and condensate.
There's also pumping costs to consider. Typically, municipal or plant water pressure pushes water through the softeners. This pressure will typically also get it into the DA. If the make-up is dumped into a vented condensate tank, it's pressure goes to atmospheric, and all of this water has to be pumped into the DA.
I've never been a big fan of coatings for tanks. I've seen too many coatings crack or split, allowing water to get between the coating and the tank, resulting in some serious corrosion between the layers. And the corrosion rate of carbon steel exposed to cold make-up water that's full of dissolved oxygen getting mixed with hot condensate, is just spectacular.
There are other issues of adding make-up water to the deaerator instead of to the condensate tank.  ONe is the retention time and how you are going to control putting condensate into the deaerator and how you are going to control putting make-up water into the deaerator?  Typically, if water is coming from two different sources identical set of controls need to be added to the deaerator where only one set is required.  This would include an additional level control and valve.  On larger deaerators especially, this requires a higher purchase cost and more equipment means more spare parts and maintenance.  THe added pumping cost described above is negligible.  Deaerators usually have modulating feedwater valves with pumps that run continuous on the surge tank feeding the deaerator.  The pump is running anyhow and would not add any additional pumping cost.
Another disadvantage is if a large amount of make-up water is added to a hot deaerator it can cause a vacuum in the tank.  Although all deaerators should have some sort of vacuum protection it is not good for the system or the installation.  Some vacuums can cause violent reactions with piping.  Spray deaerators, generally, cannot react fast enough to properly change from hot condensate to cold make-up water for proper deaeration.  Tray types are a little better but not recommended.  Even the PTC for deaerators recommend steady loads.  THis makes the deaerator work more efficient and keeps the system steady.  Adding a large amount of cold make-up also takes its toll on required steam that comes from your main steam line.  All of a sudden the dearator is demanding more steam.  If it is drastic enough the deaerator will lose pressure and possibly vacuum which will make worsen the steam demand instantaneously.  THis steam has to come from somewhere and will rob another place for it.  The boiler certainly cannot act fast enough for an istantaneous demand.  What I am trying to say is that it can effect the entire system.  The best thing for a steam system is trying to keep it as steady as possible and this is true throughout the system.
As far as coatings on surge tanks... the returned condensate will also have dissolved oxygen once exposed to atmospheric conditions.  Return condensate at 133F, for example, will have approximately 5 ppm of dissolved oxygen at atmospheric conditions.  While it is true the make-up water will have more the tank is still being attacked.  It does not take much dissolved oxygen to cause a pin hole in carbon steel.  Personally, I am in favor of lining boiler feed or surge tanks.  If applied properly it makes the unit last longer.  Maybe the key is to have a manufacturer that can apply it properly.  There are several out there with 10 year warranties.  I have seen tanks not lined take 1-2 years to become pitted with oxygen.
To all,
Are there any water treatment or boiler operators out there that can make suggestions ?
Does anyone have experience with the premature replacement of deaerators due to problems mixing makeup water ?
Thanks to all who respond.....
MJC
In 27 years of working in a wide range of steam plants, I've never seen a DA require premature replacement due to the mixing of condensate, and cold make-up water in it. This includes a number of installations that were such a mess (they appeared to have been piped-up ramdomly) that it was incredible that they worked at all.
If the DA manufacturer is supplied with some basic information regarding the plant conditions, so that the correct model can be supplied and the installation instructions are followed, then there should be no problems.
There have been several discussion on this topic over the last while. Check the "Chemical plant design and operations" and "Heat Transfer & Thermodynamics engineering" boards on this site.